ATS for a PDP to Power Equipments

08/15/2010 10:14 AM

I have a query about ATS(Automatic transfer switches).CAn someone adv when do you use the "Break before make" and "make before break". Would the type of load be a concern when choosing the ATS. need some help with this choices.

Register to Reply
Pathfinder Tags: ATS
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: ATS for a PDP to power equipments

08/15/2010 10:53 AM

If you need to transfer the supply without the interruption of load, use make-before-break ATS. It is also called close transition switch. With this type of switch, the second source is connected before the disconnection of the first source. There is a short duration of time (generally in milli-second) when both sources remain connected together. This requires both sources in synch condition, other wise there will be short circuit between the two sources and severe damage will occur. Generally, this type of switch is required for the bypass sources of the industrial or larger size of UPS where the loads are not allowed to be interrupted.

See this thread for further help:

http://cr4.globalspec.com/thread/49698/Automatic-Transfer-Switch

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#2

Re: ATS for a PDP to power equipments

08/15/2010 11:16 AM

One thing you are going to have to consider before you put to much effort into using a closed transition switch is acceptance by the utility, they are discouraging the use of them, at least in my area, and require an extensive and sometimes ridiculously cost prohibitive amount of testing before allowing them to be put into service.

Register to Reply
Member

Join Date: Aug 2010
Posts: 6
#3

Re: ATS for a PDP to Power Equipments

08/15/2010 9:57 PM

There are two type of ATS, (i) Break before Make I.e. open transition (ii) Make before break i.e. close transition Selection of of neutral is also imp like solid neutral,switched neutral or overlapping neutral. Bypass isolation(usually for maintenance purpose) switch can be available with both options and mainly used when thr is critical loads. and difference between close transition and open transition:in close transition you need to have both source available before switching and in open transition mainly it is happens when one source fails and ATS give signals to DG to start.Before transferring from one sources to other you have to take care of in phase switching mainly when loads are motors.

Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

aamirsubhani (1); msamad (1); norton850 (1)