Dear Techies, i have to calculate the ratings of harmonic filters based on following informations: 6 units of 1600KVA UPS,380 V load will be fed via Busduct of 380V,2500A for telecom data center. Client is asking for harmonic filters in order to minimize the harmonics and heating of Busduct. Please help. thanks Aamir

Register to Reply
Pathfinder Tags: Harmonic filter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#1

Re: Ratings of Harmonic Filter

08/16/2010 1:32 AM

To size the harmonic filter, you need to identify the harmonic sources.

Then you need to check the harmonic contributions from each of the sources.

which will give you the clear idea about the harmonic order which is dominant in the system.

based on that you can select the corressponding harmonic filter, also check whether you need pf factor improvement in addition to the harmonic mitigation.

then you can select harmonic cum pf filters for your application.

you can ask the UPS supplier to give the harmonic details,

you can also ask UPS supplier to use internal 3 winding transformer and harmonic filters if UPS is still not ordered which the best way to control the harmonic at the source end.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Member

Join Date: Aug 2010
Posts: 6
#2
In reply to #1

Re: Ratings of Harmonic Filter

08/16/2010 9:21 AM

thanks, but need thumb rule if any in selecting harmonic filter

Register to Reply
Active Contributor

Join Date: Nov 2009
Location: Mumbai
Posts: 17
Good Answers: 1
#3
In reply to #2

Re: Ratings of Harmonic Filter

08/16/2010 11:19 PM

There is no thumb rule as such. The subject of Harmonics itself is quite a complex one and requires accurate measurement and analysis by Experts and Certified professionals. Measurements need to be carried out at various critical points, feeders, transformers etc. The study is the first step in the direction of mitigating the harmonics problem. The next step is proper designing of the filters as per the requirement. Cheers, RV www.econserve.in

__________________
Cheers, RRV
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#4
In reply to #2

Re: Ratings of Harmonic Filter

08/17/2010 1:20 AM

it better to ask UPS supplier to provide the inbuilt filters inside the UPS

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #2

Re: Ratings of Harmonic Filter

08/17/2010 11:13 AM

Thumb Rule??? That too for such a complex phenomenon called "harmonics". I am really scared.

I advise that you take up a power quality study of your installation, fing out the dominant harmonics then decide the filter.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5

Re: Ratings of Harmonic Filter

08/17/2010 9:29 AM

Remember that as with any filtering scheme, the harmonics current (ITHD) will only be reduced upstream of the filter. The harmonics current (ITHD) will not change by much between the load and the filter connection. This is because the harmonic current cancelling is done where the filter current "meets" the load current. Depending on where you connect your filter, it might not reduce the harmonics current in the bus-work.

This is in contrast with the harmonics voltage (VTHD) will be reduced on all the power feeder.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Member

Join Date: Aug 2010
Posts: 6
#7

Re: Ratings of Harmonic Filter

08/18/2010 5:17 PM

Thanks for all suggestions. Problem with me that harmonic filter is coming inbulit with the UPS. Even though the consultant is asking for it. All loads are through tapp-offs breaker of Busduct and it is very tough to put the harmonic filter at each load point(11 tap-offs points for each run,total 6 runs) Type of loads are computers. i have a solution guys but i dont know wether ir will work or not,to get the ratings of harmonic filter installed in UPS and using this same filter at source point of Busduct. please suggest. thanks Aamir

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#8
In reply to #7

Re: Ratings of Harmonic Filter

08/18/2010 5:50 PM

Please, send a single line diagram. Your description is not obvious.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#9
In reply to #7

Re: Ratings of Harmonic Filter

08/19/2010 1:04 AM

if ups having in built filter justify to the consultant that the harmonics injection from the the UPS are reduced at the UPS end only. Give him the harmonic report

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#10

Re: Ratings of Harmonic Filter

03/13/2011 1:23 AM

seemed i had same trouble

__________________
One system
Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

aamirsubhani (2); electricalexpert65 (1); loadshare (1); marcot (2); rrv (1); sms149 (3)

Previous in Forum: Voltage   Next in Forum: Battery Resistance

Advertisement