Dear sir,
Good day to you,
I have 3phase/4wire CT operated energymeter i don know how to calculate kwh consumption CT RATIO-1600/5A.so kindly explain to me how to calculate.
Regards,
Karthi,
Reliance Foundries ltd,
Botswana
CR4 Admin: From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.
Re: Reg:KWH Calculation
08/19/2010 12:56 PM
CT RATIO 1600/5A = 320 multiplier. Read the KWH's from the meter and multiply by 320 for the total. EG meter reading = 1000 kwh x 320 = 320000 kwh's
I assume you have no PT's.
Good Answers: 244
08/19/2010 7:12 PM
This is not always true, there are other factors needs to be considered for getting the correct multiplying factor.
See this thread for the details about the energy meter Multiplying Factor:
http://cr4.globalspec.com/thread/36700/M-F-in-Electricity-bill
- MS
08/20/2010 8:04 AM
P=VIcosfi
U current And voltage of supply and take p.F 0.8 ..........u ca easily find power with o
Reply Score 1 for Off Topic
08/21/2010 6:25 AM
NORMALLY the energymeter is rated for a specific CT Ratio: that is, there will be a recommended CT ratio for it, or, if it is programmable, you set it for a particular CT ratio. THEN the displayed value of kWh is the acctual consumption either for a period (if the meter is displaying the cumulative consumption) or the Instanteneous consumption if displaying such. If it is a digital meter, ther will be a p?button to set the display for either. You don't need to ca;lculate or multiply anything UNLESS the CT used is different from the required CT ration for the meter(setting) in use. then it is a matter of converting the values using the old rule of 3 in math...