Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 5:21 AM

I have a transformer that is connected to 33kv switch gear,precisely 4 months ago the transformer went out of service and the fault shown on the switch gear was "TR GAS" meaning transformer gas.After careful examination i realized that when i removed the control cable for transformer gas and pressure from the transformer the fault cleared from the screen of the switch but the main issue now is that the insulation resistance test that was conducted gave a zero value; this value is grossly wrong and so, I decided to heat the coils of the transformer via the copper bars at the secondary and the meggered value is still zero. Is it possible the oil is contaminated or is are the windings faulty? Right now am not sure of what to do. Can anybody help me with ideas

Transformer Spec

2500KVA

33kv/415v

ONAN cooling

50hz

connection: D yn11

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2010
Posts: 15
#1

Re: Transformer faulty

09/03/2010 6:09 AM

Hi

What are the measured values ie HT to ground, HT to LT, LT phase to ground.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 7:51 AM

You heated the LV terminals? All you are going to do by doing that is damage the LV bushings where they enter the tank.

I take it you tested the LV terminals to earth, did you disconnect the neutral / earth link first?

Get an engineer in that knows what they are doing before you cause more problems.

(Got to admit though disconnecting the alarm is a sure fire way of getting it to go away)

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 9:42 AM

I agree with TonyS - you need to have someone qualified test the transformer for what caused the gas. The usual culprit is an internal arcing fault of some sort. On a transformer that small, that's the only thing likely to trip a fault pressure relay (educated guess here of what detected the gas).

If insulation resistance really is zero ohms, your winding is shorted to ground, unless you left the neutral link on a wye-connected winding in place. That just doesn't go away on its own. This transformer may be toast.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#5
In reply to #3

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 12:00 PM

A big thank you to everybody,i just checked out the transformer and realized the windings are shorted to ground.Anyway, i have taken a sample of the oil to send to a more qualified engineer to examine; but from physical inspection the transfromer oil has been contaminated. Thanks

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 12:56 PM

Yes, the oil is probably contaminated, but that is not the real problem. Whatever caused the contamination (in this case, the winding fault) is the problem. That will probably require detanking the transformer core & coils for inspection and rewinding. Depending on the time and cost of that, you may find it is more economical to buy a replacement transformer.

The best that the oil analysis can do is suggest the nature of the fault, and I'm expecting if the winding is shorted it will show arcing products (acetylene, ethylene, plus carbon soot and metal particles).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/03/2010 10:17 AM

Low oil level can give transformer gas alarm if the level falls below the Buchholtz float. It would be ironic to have a transformer out of service for 4 months for the sake of a few gallons of oil.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#7

Re: Transformer Faulty - Fault Shown is "TR GAS"

09/04/2010 1:30 AM

carefull with this. I've seen a lot of transformer damaged caused by insulation failure. The pressure switch and buccholz often indicates an insulation failure. The megger test is already a good indication that there is an insulation failure.

Do you have a TTR (Transformer Turns Ratio tester)? This is a very good tool in checking if you have a turn-to-turns short. Also, a DGA will help you which part of the transformer failed.

Dant

Register to Reply