Circuit Tripping

09/05/2010 1:56 PM

In my company, Whenever we change over from one dg set to another or whenever the mains supply gets changed over to Stand by suply, there occurs a tripping in the RCCB in main essential panel of our switch room.Is this related to any problems in DG side or is it related to load side problem. Pls help Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#1

Re: Circuit Tripping

09/05/2010 8:37 PM

It sounds like phase angle crossing where the transfer is taking place so fast that the sources are out of phase, you can either slow down the transfer and let the load decay or use an in-phase monitor to prevent out of phase transferring. If you go with an in-phase monitor be sure it has a dead bus feature or it won't operate on a power failure. Its not a big problem.

Register to Reply
Anonymous Poster
#2

Re: Circuit Tripping

09/05/2010 10:42 PM

dg set nuteral need to conect earth

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#3

Re: Circuit Tripping

09/06/2010 1:21 AM

check governors...and go with no.2...slow down your load transferring..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#4

Re: Circuit Tripping

09/06/2010 1:24 AM

Check the DG set panel program. Cheek the earthling. Check the load distribution .

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#5
In reply to #4

Re: Circuit Tripping

09/06/2010 1:49 AM

check the earthing of the your DG system and recheck the earth fault relay settings

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#6

Re: Circuit Tripping

09/06/2010 3:21 AM

It may be out of phase as said by norton850, as RCCB tripping means there is large out of phase you have to slow down the transfer rate considerably to avoid such a situation, also check the Dg earthing if the earthing is having a leak some where. if you are having an auto changeover system, do the changeover manually and check the voltage in each phase and then allow the changeover, by doing this way we can examine the exact areas as where is the real problem of the system.

your synchronising panel also to be checked for exact settings.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Circuit Tripping

09/06/2010 12:58 PM

first, Make sure that all the DG alternators have their neutrals to earth, separately (different eart pits...)

2nd, Check that in your wiring system, none of the neutral wires is leaking to earth (damaged insulation and contacting metal bodies that will be earthed...).

3rd, If you have a lot of surge suppressors connected in your circuitry on electronic dc supplies, some have capacitors connected to the earth and either the neutral or phases. If discharged, when energising, they draw a substantial current to ground and may trip the RCCB. All depends on the ratings and the current surge.

Register to Reply
Participant

Join Date: Sep 2010
Location: Hubli ,Karnataka,India
Posts: 3
#11
In reply to #7

Re: Circuit Tripping

09/30/2010 11:51 AM

I did check the earthing of neutral of our main Dg ie 125 KVA one.As such there are no loose connections.But when i measured the earth resistance value, it came to a very high one ie 12.5. Can this be a major cause for the tripping of RCCB? Thanks in advance

Register to Reply
Anonymous Poster
#8

Re: Circuit Tripping

09/07/2010 2:08 AM

Change your company and join where there is no tripping problems.

Register to Reply Off Topic (Score 3)
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#9
In reply to #8

Re: Circuit Tripping

09/07/2010 4:45 AM

This is a Good Technical forum, why are you posting such nuisance comments and that to as a Guest.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10

Re: Circuit Tripping

09/11/2010 10:00 PM

If this is "On-load" changeover, then there could be out-of-balance currents due to motor inrush currents.