Need some help to confirm if the relay contacts in the link below can handle .5 amp @ 120VAC. The contacts of the relay wire to a Quantum Digital input module. The data sheet shows inductive loads for make and break. I'm using this relay to wire to a digital input module which I believe is a resistive load. I believe this is not an issue just need some confirmation.
http://samplecode.rockwellautomation.com/idc/groups/literature/documents/pp/700-pp020_-en-p.pdf
Re: Relay Clarification
09/08/2010 3:35 AM
Forgot to mention I'll follow up with manufacturer.
Good Answers: 181
09/08/2010 3:57 AM
You'll have no problem with the relay.
Just out of interest what are you using a Quantum PLC or drive.
09/08/2010 4:19 AM
The bit of the datasheet with the table of current-handling is a bit confusing - the "Make/Break" section is refering to DC only.
The important reference is "B300" (you'll find it listed in table 5 on page 1-40 of the Safety Products catalog, which also gives Utilization Category details).
As Tony said, you'll have no problem.
09/08/2010 11:34 AM
YES!
CARPE CRUSTULORUM!
Good Answers: 18
09/09/2010 2:02 AM
You'll have no problem, but make sure the resistance of the relay contacts dont interfere with the required resistance of your load. However the manufacturer is your best bet.