How Many mmsq Aluminium 4 Core for 60 KVA 3phase 400V 50 Hz

09/18/2010 9:50 AM

I need to connect a 60 KVA load to source of 400V 3phase about 20 mts away by a four core aluminium unarmoured cable open to air. Ambient temp. reaches to a max. of 50 degree celcius. How many sqmm cable should be used?

Register to Reply
Pathfinder Tags: aluminium cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: How Many mmsq Aluminium 4 Core for 60 KVA 3phase 400V 50 Hz

09/18/2010 2:16 PM

Have you looked in the ratings table? The answers in them!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#2

Re: How Many mmsq Aluminium 4 Core for 60 KVA 3phase 400V 50 Hz

09/21/2010 2:12 AM

Minimum 95 mm2, if derating factor on proximity with other cables is considered. If it is to be laid alone with no possibility of other cables being laid with it in future, then you may go for 70 mm2. Check the cable catalogue also.

BB Raina

Register to Reply
Participant

Join Date: Sep 2010
Posts: 2
#3
In reply to #2

Re: How Many mmsq Aluminium 4 Core for 60 KVA 3phase 400V 50 Hz

09/21/2010 5:01 AM

Thanks.