Generators

09/18/2010 11:08 AM

hi friends

we have generator 4750kva,3phase-700v,50hz.gen.bearing oil entered the generator due to seal defect and windings were damaged.i am looking for explaination for what electrical happend and why C.B. did not tripped TO PROTECT THE GEN.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Generators

09/18/2010 1:06 PM

What were the protection devices on the generator?

The Earth fault protection should have activated.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2

Re: Generators

09/18/2010 1:59 PM

What is the nature of the damage? What test failure? Oil contamination causes deterioration/breakdown of insulation.

__________________
CRTL-Z
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Generators

09/18/2010 2:31 PM

Opening the ACB wouldn't stop the damage, it would just stop any parallel back feeds causing more damage. The engine and excitation needed to stop.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#4

Re: Generators

09/19/2010 12:24 AM

You are looking in the wrong direction; It is the level or flow sensers in the bering oil circulating system which did not not warn appropriately, so trace that out.

Has the Operators being monitoring the bearing temperature, Deviation from normal operating temperature would have given clue to a vigilant Operator.

Bearing oil is insulator so rotor earh fault cannot be sensed by the rotor relay, Other protections like Differential and Interturn will operate only when winding has been dammaged.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: Generators

09/20/2010 7:32 AM

Most oils contain traces of sulphur. (remember the bad smell of burned oil in a gear)

When an electrical winding is covered with oil and this winding is at normal operating temperature (+/- 80 ° Celsius), the sulphur destroys the insulation of the cupper wires.

It is a process that takes several months before there is a break down in isolation.

But finally the windings will get in short circuit.

Mostly the coils have changed colour at the places that where immersed in oil.

Solution, they sell lubricants with no sulphur, they are used in conveyer motors, and hermetic sealed compressor motors.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#6

Re: Generators

09/20/2010 7:35 PM

Please furnish further details about the protection scheme used for the generator. Also give the details of type of winding insulation. As rightly stated in one of the comments, oil is also a type of insulation. But in case of open circuit ventilation of the generator, lot of dust, carbon particles and other contaminants enter the generator and penetrate into the insulation (unless it is epoxy insulation) and provides tracking paths to earth, other phases and/ or to turns of the same phase. If inter turn short protection is not provided then any short between turns would result in circulating current and then in charring of coil insulation.

You have not indicated how much of oil has entered in the generator. If the terminal housing is flooded, then phase to phase, 3phase short or earth fault can also take place. Normally bottom of the generator casing is given some slop such that any liquid entering the generator gets collected there and a liquid detector gives an alarm. Whether such an arrangement exits in your generator?

May be I can further analyze it if details as asked above are given

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); mountk2 (1); pcchatur (1); rudy.leurs (1); TonyS (1); Unredundant (1)