Is it really difficult to understand excitation current required for AC generator for a enthusiastic mechanical engineer? Can some expert guide in this regard. Let us be specific, I wanted to learn what should be rating of a excitation cubical for 50 MVA generator operating at 200 RPM. Please assume typical electrical data if any other required.
Good Answers: 804
Re: Excitation Current of AC Generator ?
09/20/2010 12:56 PM
No such thing as "typical" unfortunately. You don't say what kind of "generator" but I suppose we can ASS-U-Me synchronous by virtue of the 200RPM? Still, self excited or externally excited? Brushless? What do you mean by "cubical"?
09/21/2010 3:08 AM
I guess he means "cubicle".
Guest,
an excitation cubicle for a 50 MW alternator could include PT's for AC voltage sensing,
a DC power converter, CT's for droop and PF control, AVR to regulate AC voltage, electronic for parallel control and much more.....
does it still look complicated for a mechanical engineer?
dont say it, write it
09/21/2010 3:25 AM
not really, please proceed further to calculate (dc)field current & voltage rating of excitation cubicle.
09/21/2010 3:21 AM
Regret for typographical error. It is cubicle (excitation panel).
Other related information is :
Synchronous generator 50 MVA, externally excited, 13.8 Kv, 50 Hz, Cos phi 0.9.RPM 200,
How to calculate required (DC) field current and voltage rating of excitation panel ?
09/21/2010 3:47 AM
Nothing to calculate, you have to check with the manufacturer....
Or you can inject a small DC voltage and check the output voltage ( you need PT's) and than increase this DC till you reach 13.8 KV, this is the MINIMUM DC voltage you need for the excitation at no load , at full load it is much higher, 4 to 5 times, for the current you can measure the resistance of the field coil and calculate the required current as per DC voltage needed