Previous in Forum: electrical energy   Next in Forum: 3P Capacitor Bank
Close
Close
Close
Rate Comments: Nested
Anonymous Poster

PT Testing for Resistance

09/20/2010 11:46 PM

Do anyone know how a PT testing is done inorder to find resistance in each wingings of a Ynd 11KV/190V,100KVA. I guess its SC test as we do normally in a transformer but anyone who is familiar with PT testing?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: PT Testing for Resistance

09/22/2010 9:04 AM

DC winding resistance of a PT is done the same as with a power transformer - apply a DC current to the winding (not more than the winding will handle!) and measure the voltage with a digital multimeter. Ohms Law gives the resulting resistance.

Is your PT 100kVA, or 100VA? Be careful - there's a big difference in current! If it's 100VA, you can probably measure the resistance directly with the DMM.

__________________
To get the right answers, first you need to ask the right questions.