Over Load and Over Current

09/24/2010 5:15 PM

please help me in explaining the difference between over load and over current protection and their settings in motor protection

Register to Reply
Pathfinder Tags: over load and over current
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Over Load and Over Current

09/24/2010 9:15 PM

A good way to think is -

Overcurrent is any higher-than-normal current, includes Overload and Short-circuit.

An overload is an overcurrent flowing through the intended path.

A short-circuit is an overcurrent flowing through an unintended path.

Specific to motor protection, overload protection is given by an overload relay, set at rated FLA in IEC countries (maybe different in North America), and Short-circuit protection is provided by fuses or circuit breakers, selected as per Type 1 or 2 coordination.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: Over Load and Over Current

09/24/2010 9:32 PM

Over Current is more generic term. It is categorized as Overload Current and Short Circuit Current.

Over Load Current: The term overload is applicable mostly for motor loads. It is generally the current when motor is overloaded by some reason. Overload can be sustained for certain period of time. There should be separate overload protection in this case.

Short Circuit Current: It is due to the fault (line to line, line to ground) in the circuit and applies to all type of circuit. The circuit should be isolated immediately. Motor starter should have short circuit current protection in addition to overload current protection.

The setting of motor Overload and Short Circuit current depends on the standard used. Per NEC article 430.32, the maximum overload setting is generally 1.15% (1.25% for motor of service factor greater than 1.15) of name plate full current and per NEC 430.52, the maximum short circuit setting is generally 800% for instantaneous trip breaker and 250% for inverse time breaker. However, the settings depend on many other factors.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2010
Location: United Arab Emirates
Posts: 12
Good Answers: 2
#3

Re: Over Load and Over Current

09/25/2010 12:51 AM

Overload relays are provided to protect the motor from overload currents .When current is too high for too long, heaters open the relay contacts carrying current to the coil of the contactor. When the contacts open, the contactor coil de-energizes, which results in an interruption of the main power to the motor.

Overload relays and their heaters belong to one of three classes, depending on the time it takes for them to respond to an overload in the motor. The overload relay itself will have markings to indicate which class it belongs to. These include Class 10, 20, and 30. The class number indicates the response time (in seconds). An unmarked overload relay is always Class 20. Typical NEMA-rated overload relays are Class 20, but you can adjust many of them about 15% above or below their normal trip current. IEC relays are usually Class 10, and you can usually adjust them to 50% above their normal trip current.

The overcurrent protection is provided by circuit breakers.Circuit breakers are usually Rated for ampere, voltage and fault current interruption rating.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Over Load and Over Current

09/25/2010 11:33 PM

Over load is always thermal related. Please remember that a motor can get overloaded even when it is drawing less than its full load rated current, if the cooling is poor. Alternately, even if a motor is drawing higher than its rated full load current, it may still not damage, provided the cooling is better. To say that overload is may or may not be related to over current. So, a overload setting for a motor should be "Thremal Overload Setting" rather than Over current Setting.

Whereas Overcurrent is always current related. It may or may not provide overload protection.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#5

Re: Over Load and Over Current

09/25/2010 11:47 PM

thank Q Mr. electricalexpert65 for your simple explanation which has cleared my doubt.

Register to Reply Off Topic (Score 5)
Associate

Join Date: Mar 2010
Posts: 28
#6

Re: Over Load and Over Current

09/26/2010 12:23 AM

THANK Q Mr. electricalexpert65 for your simple explanation which has cleared my doubt

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); kvsridhar (1); msamad (1); Tanuja (1); venu kodeboyina (1)