Io - Pick-up Setting of the Earth Fault Relay or Release
Ir - Pick-up setting of the Overload Relay or Release
Im = Making Current (I think it should be 'Icm' - Short Circuit Making Current)
Icu = Rated Ultimate Short Circuit Breaking Current (means that the Breaker can break the designated Rated Ultimate Short Circuit Breaking Current for 2 times (i.e.) in an O-CO duty; after this the breaker cannot be continued in Service and must be replaced immediately)
Ics = Rated Service Short Circuit Breaking Current (means that the breaker can break the designated rated service short circuit breaking current for 3 times (i.e.) in an O-CO-CO duty; after this, the breaker can still be used as a switch-cum-isolator, till replacement is arranged; but, it cannot break anymore short circuit current; one must have some short of short circuit back up device like HRC Fuses, then.
Ics can either be 25% of Icu or 50% or 75% or 100% of Icu.