Protections for 4 MVA 3 Winding Transformer

09/26/2010 3:19 PM

Hi

Could anyone please suggest me what are the recommended protections for the 4MVA transformer. Few 4 MVA transformers installed in our plant are given with phase over current and neutral side over current protection (51N). I would like to know whether differential protection for 4 MVA transformers is mandatory or not. Another point I would like to know is whether REF and Neutral over current (51N) both will do almost the same function or REF is faster and more reliable.

Regards

Manish

Register to Reply
Pathfinder Tags: Transformer Protection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Protections for 4 MVA 3 Winding Transformer

09/27/2010 12:47 AM
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Protections for 4 MVA 3 Winding Transformer

09/27/2010 7:29 AM

You don't state the secondary voltage.

REF for LV to protect the transformer where there is liable to be load on the neutral.

I take it you do mean neutral - earth over current for HV where the neutral isn't utilised, it protects the load. If possible REF as well to protect the transformer.

I've installed a few transformers where there's no switchgear or protection between the transformer and load on the secondary side other than neutral over current.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Protections for 4 MVA 3 Winding Transformer

09/27/2010 10:16 PM

Even though IE Rule (Rule 64A, Sub-rule 2 (d)) mandates Differential Protection only for transformers of capacity above 10MVA, it is prudent to go for Differential Protection for your 4MVA Transformer too, considering the repair/replacement costs & production downtime costs.

As for your second question, your 51N will also respond for external earthfaults whereas REF (64R) will respond only to internal earthfaults. Also, 51 N will have to have a time delay setting to co-ordinate with downstream relays and the 64R should have no time delay; it must be instantaneous. Definitely REF is faster, but only for internal earthfaults.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2010
Posts: 4
#4
In reply to #3

Re: Protections for 4 MVA 3 Winding Transformer

10/01/2010 4:41 PM

Thanks Mr. Expert (GURU), the reply forwarded by you is very much appreciated. I would like to clear one point from you is that how would you rate the protection of a transformer of rating 4MVA without differential and REF. As you mentioned that 51N is with time delay so the damage incase of fault within the transformer could lead to severe damage which can be minimized by using REF (64R) protection. Is 64R (REF) is mandatory for 4MVA transformer.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: Protections for 4 MVA 3 Winding Transformer

10/01/2010 9:31 PM

I only quoted from the Standards. Required protection is individual's choice. Generally a compromise between equipment availability and economics. If you have enough money, you may go for Differential even for a 1 MVA Transformer.

But, REF protection is mandated for transformers of rating 1 MVA and above.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (2); manishgautam81 (1); TonyS (1)

Previous in Forum: Alternator Stator E/F Protection   Next in Forum: Parallel of DC Supply

Advertisement