Double Earthing

10/13/2010 7:57 AM

what happend if we earthed ct secondary in two point in diff protection

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Double Earthing

10/13/2010 9:26 AM

Can you ask with a drawing showing the different earthing points?

Register to Reply
Participant

Join Date: Oct 2010
Posts: 2
#3
In reply to #1

Re: Double Earthing

10/14/2010 7:28 AM

I mean by two point that the secondary of LV or HV CT is earthed for examble in the marshalling box and in the protectinon pannel .

Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Double Earthing

10/13/2010 2:06 PM

Depending on where the ground points are and how long the CT circuit wires are, you may change the amount of current the relay will see in its operating or restraint coils. Consider for example the impact of the grounds as shown in the following illustration (taken from GE's "The Art & Science of Protective Relaying," with my additions of the grounds):

Look to your differential relay's instructions for the manufacturer's recommendations on grounding of the CT circuit.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); hishamageed (1); PeterT (1)

Previous in Forum: Tension and Draw Control on Paper Machine   Next in Forum: Auto-Transformer Starters

Advertisement