DG Sync Panel Instead of 4P Breaker

10/18/2010 8:05 AM

In DG synchronizing panel out going feeder, 3P breaker + for neutral using contactor why? Instead of 4P breaker using, explain why.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: DG Sync Panel Instead of 4P Breaker

10/18/2010 9:04 AM

Economy, of course! The three poles of a contactor, when parallelled can be used for a higher size neutral current than that of a 4-Pole ACB.

Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#2

Re: DG Sync Panel Instead of 4P Breaker

10/19/2010 10:44 AM

Dear sir,

Firat of all synchronizing means, parallel operation of multiple DG's as you know, in this case the neutral potential of the each DG will differ one to other, when we paralleling the DG's only one neutral should be present in the bus bar because if we connect multiple neutrals due to potential difference the control system will deduct circulating current and trip the circuit breaker immediately. hence in synchronization the neutral contactor of master DG only will be in closed condition, other follower DG's will run in floating condition. due to this only we are using 3 pole breaker + neutral contactor

Hope i cleared your doubt

__________________
Shaju Khan
Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2012
Posts: 115
#3
In reply to #2

Re: DG Sync Panel Instead of 4P Breaker

03/12/2013 7:32 AM

Dear shajahan

which relay has been used in the sync panel to open the neutral contactor

Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Muthuvel (1); user-deleted-1076 (1)

Previous in Forum: Looking for the Supply of UV Lamp   Next in Forum: Voltage Change

Advertisement