Distance Relay Testing Terms

10/21/2010 2:22 PM
plz define and

explain the following Distance relay testing terms.

1) Power swing reach test.

2) power swing blocking test.

3) switch on-to fault test.

4) PT failure test.

regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jun 2010
Posts: 4
#1

Re: Distance Relay Testing Terms

10/21/2010 4:03 PM

1.It is the region coming after the outermost zone that is beyond forward zone Z3 or reverse zone Z4.We will define this zone.Any disturbance starting above this zone setting and traversing through our defined area is a powerswing.

2.the logic is different in different relays.For Eg;in areva if disturbance takes morethan 5 ms to travel through powerswing zone it is considered as power swing and it blocks distance function

3.SOTF is enabled from the time of closure of CB and will b active upto 250 ms.If relay detects a fault within 250msafter CB closure, then relay operates in SOTF to clear the fault

4.Undervoltage detection/VT MCB Trip is given to sense VT failure and to block distance relay

Register to Reply
Participant

Join Date: Nov 2012
Posts: 3
#2
In reply to #1

Re: Distance Relay Testing Terms

11/25/2012 10:20 AM

what is zone 4 and zone 5 in a distance relay?