Cooling Towers Location

10/24/2010 6:40 AM

in HVAC system we have chillers and cooling towers and pumps I want to ask about the relation between the location of chillers and condenser pump and cooling tower:-

1- is should be locate the chillers and pumps in the same level ( what is the recommendation for this connection )

2- is should be locate the chillers below the cooling towers ( what is the recommendation for this connection )

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Cooling towers location

10/24/2010 6:45 AM

You can't be serious! You should go to school.

Procedures For HVAC System Design and Installation

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#2

Re: Cooling Towers Location

10/25/2010 1:04 AM

It all depends upon how you plan to design your plant room layout. Cooling tower is used in conjunction with water cooled condenser. The lowest temperature to which water can be cooled in a cooling towers the wet bulb temperature of air surrounding the cooling tower. It can be either natural draft or mechanical draft. There are many factors which influence the location of Cooling towers, chillers, and pumps. Few of them are Capacity and size of plant, length of the chilled water pipe lines, type of building to be air conditioned, availability of plant room space. You can refer the local code or ASHRAE standards for more details.

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Cooling Towers Location

10/25/2010 8:19 AM

This all depends on specific project.

However, without going into detail here, I would say--Cooling tower is always on roof or outside in the open.

Chiller and pumps are in the Mech. Equipment room. Also various clearances are required for maintenance of the chiller.

For specific help, u may contact me at rajk@gmx.us. Will be glad to help you

Register to Reply
Power-User

Join Date: May 2006
Posts: 142
Good Answers: 3
#4

Re: Cooling Towers Location

10/25/2010 8:38 AM

The tower should be above the pump inlet minimum 1/4" per foot fall from tower outlet to pump inlet, centrifugal pump are not self priming. Chiller elevation is only governed by static head but if you are above the tower sump you will naturally drain back to the sump and lose you chemical treatment when you overflow. If you are below the tower, every 20 storys is another 100psi of head on your condenser so you have to specify to the manufacturer. Your questions lead me to believe that paying an engineer to design this might work out to be a bargain in the ed.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5

Re: Cooling Towers Location

10/25/2010 11:05 AM

In addition to the reading suggested by lynlynch, please review this Wiki article on Legionellosis, a disease that is caused by an aquatic organism that seems to LOVE hanging around in cooling towers.

__________________
Semper Ubi Sub Ubi
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CONWAYMECH (1); Doorman (1); lyn (1); mrswamy (1)