Maintenance for Transformer

10/25/2010 12:15 AM

Hi all:

22/0.4kV - 1000kVA Transformer needs to be maintained. The last maintenance has been done 5 years ago. Below are several points to be done as raised by me.

1. Check insulation of winding

2. Check voltage ratio

3. Check oil contamination

4. Check cable insulation

5. Clean up the transformer

Is there anything else we may do for it?

Regards,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Maintenance for transformer

10/25/2010 1:23 AM

What did they do 5 years ago? Use that as a basis for your maintenance tasks.

Your points 1 & 4 can the cables be disconnected?
Point 2, why? What do you expect to find changed?
Point 3, yes do that
Point 5, clean radiators, etc. try not to damage factory-applied paintwork

Add to your checklist:
Air vent silica gel breather
Temperature sensors operate correctly
O/L and E/F can be secondary injection tested

HV / LV intertripping

To be honest there's not a lot to be done to a small transformer, they just sit there and work, or not as the case may be. If not they're not a major item to replace.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #1

Re: Maintenance for transformer

10/25/2010 9:37 AM

For 1 & 4, the insulation can be tested using DC tests (Megger / hipot / polarization index, at appropriate values). Tests on transformer windings can also include Doble insulation power factor (or dissipation factor / tan-delta) AC tests. The AC tests often give a better indicator of overall condition of the insulation, and point to areas where there is a problem (moisture, external contamination, bushings, HV winding, inter-winding, etc.)

For 3, include full battery of oil quality tests (dielectric breakdown voltage, moisture content, interfacial tension, color, clarity, acid neutralization, specific gravity at a minimum) and dissolved combustible gases (tells you if heating, arcing, corona, or other things are happening under the oil).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#2

Re: Maintenance for transformer

10/25/2010 3:06 AM

Just from the top of my head.

You can also check if Bucholtz relay (if present) is connected properly. OLTC and RTCC are properly configured. All terminating cables are in proper condition.

Regards.

__________________
The Crazy Man Talks and The Smart Man Understands
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Maintenance for transformer

10/25/2010 6:52 AM

you can also check the power factor. and if necessery can add a capacitor bank to improve the pf.

Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Maintenance for Transformer

10/25/2010 1:18 PM

From your list I would put #3 at the top. I think 5 years if too long in between checks. Maybe someone can provide a suggestion as to how long in between checks.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: Maintenance for Transformer

10/25/2010 10:10 PM

Oil tests should be done annually. Other testing typically on a 2-3 year basis, depending on how critical the transformer is, how heavily it is loaded, and what the results of the oil tests show. See the NETA (International Electrical Testing Association - www.netaworld.org) Maintenance Test Spec for information on tests and their Frequency of Maintenance Tests guide (free download) for intervals.

https://netforum.avectra.com/eweb/shopping/shopping.aspx?site=neta&prd_key=af5326f4-de81-488f-96d9-8707d514e687

https://netforum.avectra.com/eweb/shopping/shopping.aspx?site=neta&prd_key=af5326f4-de81-488f-96d9-8707d514e687

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2010
Location: currently Shanghai China
Posts: 40
Good Answers: 4
#7
In reply to #6

Re: Maintenance for Transformer

10/25/2010 11:51 PM

GA, We test the oil on all our transformers annually. We also conduct visual only inspections on the low voltage side, looking for obvious signs of heating or damage on a monthly basis.

__________________
I seek to know that which is in me, that I may know me, when next we meet.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#8

Re: Maintenance for Transformer

10/26/2010 1:33 AM

Dear Sir,

Add Transformer Oil Filtration & Testing for BDV.

Manroop.Chennai.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: Maintenance for Transformer

10/26/2010 2:25 AM

Do you have a glass container on the side of the transformer with silicon crystals in it?

If not then no worries, if you do... check the colour, and change out if more than 50% of the colour has changed and as other posts have told you test the oil.

If you change all the oil and a Bucholtz is fitted, then refill SLOWLY over a few days to allow the air trapped in the windings to escape, otherwise your TransX will trip due to air tripping the Bucholtz as the windings get warm and the air finds its way out and up.

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#10

Re: Maintenance for Transformer

10/26/2010 4:50 AM

Hi!

Since you are carrying out maintenance after 5 long years you may go for the following also:

1. DGA of oil (Dissolved Gas Analysis)

2. Carry out oil filteration

3. Replace silica jel in the Si jel breather, if not done recently.

4. BDV of oil before and after oil filteration.

BB Raina

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#11
In reply to #10

Re: Maintenance for Transformer

10/26/2010 8:43 AM

Hi all:

Thank you for your input, I remember that the oil of this transformer is checked annually. As I saw that the transformer itself is very dusty, so as a matter of fact, we need to clean its bushings. The other tricky question, how we will do this? By clean cloth or by water?

Yes, we can disconnect the cable. But it is known that we can check the insulation only. We should not do any test on this cable. Why? Because it is old and the test voltage is much higher than operating voltage. This would damage the cable, wouldn't it?

After all the work is done and the data is nice. Is that safe enough to switch power back on? Another question comes, if you were me, do you ensure that there is not any problem with energizing power to transformer? I was threaten by one colleague that he used to damage his transformer after doing maintenance. The transformer bushing is on fire after energizing. The root cause remains unknown... Yes, we don't know if it is true or not, as an experienced, what you will say to him?

Regards,

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #11

Re: Maintenance for Transformer

10/26/2010 9:42 AM

read the instructions on a firework and apply when energizing your transformer, if you are that worried about it!

As for cleaning..... use a clean cloth, NEVER water or any type of chemical cleaner

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #12

Re: Maintenance for Transformer

10/28/2010 3:41 AM

One reason I liked old GEC OCB's you could charge the closing springs then tie a lanyard to the closing lever and then clear off to safe distance. Much better than light blue touch paper and retire immediately.

Hang on I'm retired, it's coming up to November the 5th, I can't light my fireworks!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#14

Re: Maintenance for Transformer

10/28/2010 8:49 AM

Maintenance of Transformer is very much linked with the followings:

Type of Transformer - Indoor or outdoor.

Age of the Transformer.

Environment at which the transformer is operating including the load cycles.

The testing equipments/ instruments available in plant including hiring facilities.

Cmpetent Engineers/ Technicians availability.

Considering the above the following basic tests can be carried out:

IR value

PI and AI value

BDV test of insulating oil

Moisture content test of oil( Frequency Domain Spectroscopy/ DGA/ Karl Fischer Titration test)

Checking of OTI and WTI

Checking of radiator banks,diffirent valves,oil pielines.

Checking of connection in marshalling box.

Checking of Buchholz relay and OSR.

Checking of breather including silicagel.

Cable terminatins and if there are outdoor bushings the same should be checked.

Filteration of insulating oil with vacuum oil filteration plant( with 760mm of Hg.column)

Checking of winding resistances, turns ratio/ voltage ratio.

Checking of operation of OLTC/ Tap changer

Magnetic balance test,Checking of neutral grounding( if neutral is available)

Checking of functioning of M.O.G ( if fitted)

Checking of conditon transformer base wheel locking.

Checking of functioning of protective relays.

MONITORING OF SOUND DUE TO VIBRATION OF CORE IS VERY MUCH ESSENTIAL WIHCH CAN INDICATE IF THERE IS ANY LOOSENESS IN CORE STUDS AND BOLTS.

__________________
Manindra
Register to Reply
Power-User

Join Date: Jul 2008
Location: Ontario, Canada
Posts: 203
Good Answers: 6
#15

Re: Maintenance for Transformer

10/28/2010 4:39 PM

Concerning Silica Gel breathers this previous post might be of interest

http://cr4.globalspec.com/comment/312638

__________________
Faith is not blind, it is supremely reasonable.
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: