11/01/2010 2:01 PM
I am in problem with a 120 kw dc flying share motor(tmt roling mill), make parker. Problem is when rod is pass at mill speed 14 mps , it have to cut 60 meter, in encoder mode . But when it cut the leangth is not equal . We are checked encoder , motor ,plc programe all are ok. Now what i have to do?
Good Answers: 181
Re: 120 kw DC Flying Share Motor
11/01/2010 4:08 PM
First thing is to ensure the "home" datum (if it has one) is stable for the shear. If it doesn't then look for slip in the bar feed or shear drive mechanism.
11/01/2010 4:19 PM
A few questions first
do the lengths get (wrongly) longer after each cut?
does the encoder sets to '0' every cut or does it run in incremental mode?
Is the encoder fully digital (Resolver/Follower) or simply analog/digital conversion?
Is the encoder directly connected to the Mill speed (14 MPS) or does it measure separate with it's own tachogenerator?
T L.
Humans use 10% of their mind , WE take the rest
11/02/2010 1:36 AM
Actualy 120 kw motor sence with a hmd (heat seance). And we taking the encoder palses from a finishing dc motor 250 kw . I explane you. Finising motor run into 710 rpm ,then HMD . Then flying share motor 120 kw. Ok. 250 kw motor encoder continiously giving palce throug a 24 v relay board to 120 kw drive . Now when hot metal coming through 250 kw motor mount with roll. And then hmd sence then hmd give signaj to the 120 kw drive. And then 250 kw encoder palce count stard and plc give comand to cut. Ok but the leangth is not equaly when it cuting.
11/02/2010 4:57 AM
How can I ever make sense of this all ?
A crop shear ( not a flying share 120 KW)
An HMD is not a heat seance, it's a Hot Metal Detector
The Encoder Pulse (not pAlse ) from a roller on the outcoming drive 250 Kw
So from drive 250KW comes a continues encoder pulse ---> (24v relay on Crop Shear)
<Loop>
HMD detects Hot metal -----> signal to 24v Relay ---> PLC
PLC starts counting encoder Pulse
PLC counts until value , signal (cut)---> Crop shear
Crop Shear ( Cut)
<End loop>
So now the problem
the lengths vary , causes
Primary I'd say, check/callibrate the HMD for the correct temperature (we had this a few times)
second add an extra test_counter in the encoder pulsing and check the encoder Inputcard on the PLC.
Replace the 24 v relay (old ? dirty contacts ?)
Success L8rz.. TL.