Using 60Hz Transformer on 50Hz Supply

11/04/2010 7:15 PM

What happens to the voltages induced? And which values will be constant?

If voltage induced is constant it means the current will increase and this will probably lead to saturation at core, true?

İf current increases it will slightly cause a voltage drop on primary and the voltage induced will decrease. What is the final value considering the assumption above? (flux ,and then current increases due to the decrease in frequency)

Or the voltage induced is not constant?

What would be our leading assumptions while trying to understand this case?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Using 60Hz Transformer on 50Hz Supply

11/04/2010 9:16 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
3
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: Using 60Hz Transformer on 50Hz Supply

11/06/2010 8:01 AM

As suggested by MSAMAD, check the previous thread.

To add clarity, it is the revers of what was on the thread. i.e. from 60 to 50 Hz, your tansformer Impedence will drop by 20%, therefore increasing the primary current and could saturate the core by having a higher flux. If saturation occurs, then the current flow in the primary can increase even higher and overheat.

Usually, saturation will not happen on the lower end of the loading: that is if you do not load the transformer to its max rated watts. 80% less than the max load will still be safe, even though it will run hotter when compared to the same load on 60 Hz. Keep it at 70% better.

From the voltage ratio transformed, the same ratio will remain between the primary and secondary since this depends on the number of turns in each winding.

If possible, you can use the transformer on 50 Hz if the voltage on 50Hz is lower that the one on 60 Hz in the range of 20% less.ex: if 115V at 60Hz, then 95V at 50Hz. or 140V at 60Hz then 110V at 50Hz.

Register to Reply Good Answer (Score 3)
2
Guru
Popular Science - Weaponology - New Member Engineering Fields - Engineering Physics - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Dec 2007
Location: No. VA, USA (No, it does NOTu mean "won't go"!)
Posts: 1796
Good Answers: 75
#3

Re: Using 60Hz Transformer on 50Hz Supply

11/06/2010 10:38 AM

The first answers assumed you were talking about a large scale power handling project, such as a municipal power source. They may be right. If so, what I have to say is less useful, if at all. But, if what you are looking for is more in the small power realm (say in the building of a small electronic device, such as an amplifier, or even a battery charger, and if you aren't using a transformer where you are likely to approach its maximum power handling capability, the frequency of the input voltage should not affect its current out, and, since as noted, voltage induced is directly a result of turns ratios, there should be no measurable affect. NOTE, I did say that this is if, worst case, you are not approaching the power limits of the transformer. At low power usage, (80%, as noted, is a good upper limit, but unless the transformer is VERY small, such as a PCB mount bobbin style transformer, even 90-95% has caused no heating in my experience), the effective parameter is capacitance, which, coupled with the innate inductance of the transformer, adds to the reactance, and changes its resonant frequency. But reactance, at 50-60 Hz, is usually so low as to negligible in its affect on low power transformers.

Hope this is useful, but remember, THIS only helps if you are working at "hobby" power levels. If you start pushing any inductive device to near its full rated power, reactance changes caused by input frequency become a potential source of disaster. Derate and succeed!

__________________
Been away a while. Miss all my old friends. Some of you I KNOW are still around. Where are the rest?
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Dec 2007
Location: Chicago, IL, USSA
Posts: 141
Good Answers: 3
#4

Re: Using 60Hz Transformer on 50Hz Supply

11/08/2010 4:59 PM

When a 60hz transformer is used at 50Hz the transformers core will over heat due to increaesd magnetic flux in the transformers core. You can use a 60hz transformer at 50hz but the input voltage can only be 83.3% of nominal input rating and the transformer KVA capacity must be reduce by 83.3% (5/6) also; keep in mind when the primary voltage is reduced the secondary voltage will be reduced by the same % because the transformers turns ratio N1/N2 remains constant. In addition to the heat the transformer also will have increased vibration and audible noise.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#5
In reply to #4

Re: Using 60Hz Transformer on 50Hz Supply

11/09/2010 6:18 PM

I dont agree that vibration and noise increases, They must decrease..

__________________
jinxnao
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Apps Man (1); jinxnao (1); LAA_Lucke (1); micahd02 (1); msamad (1)

Previous in Forum: Voltage Step Down Using Resistors   Next in Forum: DC Fast Charger Consumption Equivalent

Advertisement