Can you tell me what are the parameters in choosing a protection relay for a 11kV system. What calculations do i need? and what kind of protection would i need.
Re: Protection Relay
11/07/2010 7:34 AM
NEC, if USA.
I'd double up on the protection. You never know what you'll be exposed to these days.
11/08/2010 1:41 AM
There are many things that you should consider the following are some important technical parameters that may help:
1. Protection functions that you need to implement (over-current,earth fault,under- voltage etc...)
2. Input impedance to ensure correct VA rating of the CT is specified
3. Sensitivity of relay
4. Self supervision functionality
5. Input Current/Voltage ratings
6. Supply voltage
Good luck!
Omar Aziz