Hydrotesting of Gas Flow Lines

11/09/2010 12:18 AM

Can any body help me out for calculating the hydrotesting pump capacity and comtressor requirement:

1) Calculations for selecting hydrotesting pump

2) Calculations for pump required for filling of lines having head of 40 meters

3) Capacity of compressor required for dewatering of 20KM 10" line having head of 40 meter.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#1

Re: Hydrotesting of Gas Flow Lines

11/17/2010 2:57 AM

The most important parameter is missing in your question i.e. the "test pressure". It is required question (1).

1) Hydrotesting pump should be of plunger type positive displacement pump. To decide about capacity, use the thumb rule as follows:

"Approximately 10 litre water is to be pushed in 10 cu.m volume to increase the pressure by 10 bar."

Your volume is about 1000 cu.m. Depending on the test pressure, calculate how much water is to be pushed. This will give required pump capacity per hour.

2) Take a centrifugal pump of 60 m head. Capacity you can decide by the time available for filling the required volume. Keep a vent at the highest point in open condition while filling.

3) A small compressor of any type with a delevery pressure of 5 bar is OK. Capacity depends on how fast you want dewatering. Compressed air is to be connected at the vent at the highest point.