Lighting in Mining Area

11/10/2010 5:24 AM

Dear Sir, As per Indian Electricity rule surface mining area and open cast mining area power supply for the lighting shall not be exceed 250 V (L-L) and neutral point shall be solidly earthed. I have 415 V, 3 Phase supply, to fulfill the above requirement I have to use 415/240 V (L-L) 3 Phase transformer. Why this is required? what are advantages of this system. Instead of above can I use 415/415 V lighting transformer? In that case lighting supply will be 240 v (L-N). Thanks

__________________
manirul
Register to Reply
Pathfinder Tags: Lighting in mining area
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Lighting in mining area

11/10/2010 8:59 AM

In the said 415V/240V (L-L) Lighting Transformer, the secondary (240V) side will normally be a centre-tapped one with the centre point solidly earthed. With such an arrangement, your 240 V lighting will still have a working voltage of 240 V; at the same time, the shock risk is reduced as the phase to neutral/earth voltage (touch voltage) is only 120V now.

Register to Reply Good Answer (Score 4)