The 37 KW motor starts in star and converts to delta, the contactor (delta closes). But, the motor does not run (the delta and main contactor is not tripping though). We have checked the running individually by starting in star and directly starting in delta. it runs that time. but in normal star/delta fashion the motor trips in delta change over. what could be the reason?
Good Answers: 804
Re: star delta motor running trouble
11/12/2010 1:32 PM
MOTORS don't "trip", contactors don't trip either, but protective devices FOR the motor might trip. So what exactly is tripping?
Re: Star Delta Motor Running Trouble
11/13/2010 11:07 PM
check the star/delta timer then somewhat adjust the timing of that timer.
Good Answers: 170
11/15/2010 9:20 AM
Wrong Power Cable Connections
India - Member - New Member Engineering Fields - Electrical Engineering - New Member
11/18/2010 8:26 PM
I hope the motor is a squirrel cage IM.You might have observed the motor runs little slow when it is in delta and works fine in star.please check the connection of delta is done properly(both starter and links outside the motor).If the problem persist its because entire motor winding may be wrongly winded.I hope back-off fuse setting is correct.
11/20/2010 10:04 PM
connection may be wrong.