Re-energise an Old Newage 250 KVA Generator?

11/12/2010 4:07 PM

This is a 1969 Dorman engined 250 KVA 415 volt 3 phase stand by generator unit, ex local utility company.

The engine runs fine and the frequency meter is responding correctly to engine revs, but the unit is not producing any voltage. However, the generator voltmeter is sometimes flicking off 0 and sometimetimes up towards 400v. Last serviced about 5 years ago, untouched since.

The unit has a separate small ac generator inside at the back end. Its field coils appear to be fed from the stator output. The small generator output goes through diodes on a plate on the shaft and into the rotor.

I assume the there is meant to be enough residual magnetism to start the generation.

Do I need to flash it to re-energise it? If so how do I do this safely?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Re-energise an old Newage 250 KVA generator?

11/12/2010 4:31 PM

"Dorman engined" or did you mean "LyndoorTM engined"? sorry couldn't help myself, its Friday afternoon

Have you checked the output of the "separate small ac generator inside at the back end" from the output terminals of the small AC gen, through the diodes to the rotor?

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Member

Join Date: Nov 2010
Location: Orkney, Scotland
Posts: 6
#3
In reply to #1

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 4:12 AM

Hi

It really does have a Dorman engine - proudly says all british made.

Please how do I get to check the output of the small ac generator. its output coils and diodes are on the spinning shaft.

There is a bakelite? box mounted on its field coils.

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#6
In reply to #3

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 8:58 AM

Westray,

"Please how do I get to check the output of the small ac generator"

Use a multimeter.

KJK

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Anonymous Poster
#2

Re: Re-energise an old Newage 250 KVA generator?

11/12/2010 11:11 PM

Please check all wiring of excitation system for loose connection. Measure voltage directly on alternator terminals using a multimeter.

For verifying if the exciting system if working properly, you must disconnect the automatic voltage regulator (all connections) and apply a 12V DC on the alternator field and check if voltage is obtained. And then you can have an idea about the problem.

Register to Reply
Member

Join Date: Nov 2010
Location: Orkney, Scotland
Posts: 6
#4
In reply to #2

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 4:25 AM

Hi and thanks for the help.

The alternator terminals are in heavy case above the alternator tight under the fuel tank. Not sure how I get to them without dismantling a lot. However I could get to the other ends of the cables inside the control box.

The exciter alternator has a bakelite? box mounted on the field coils. is this the AVR? I have not tried to open it up yet, as it is not obvious how it opens. It looks like there might be 2 small trimmer screws on the cover.

On the outside of this cover is a glass fuse (intact) a resistance and some connections.

The control box instructions say "hold overide button in to start and wait for the safety circuit light to come on". It starts fine but this safety circuit light does not come on and none of the lights to indicate under or over voltage etc come on.

I am going to look inside the control box next in the hope there is a relay that is not making contact after starting up. Could the exciter circuit be disabled until the safety circuit has come on?

Register to Reply
5
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #4

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 8:36 AM

You have a brushless alternator.

The small generator at the end is called the Exciter.

The Main Alternator has its Own Field winding on the rotor and it is fed by the Rotor winding of the exciter. This rotor winding is 3 phase and supplies a 3 phase bridge rectifier fixed on the rotor. The rectified dc is then sent to the main field winding.

the AVR receives power from the main 3 phase winding and rectifies it to dc before feeding the exciter field coil which is the stator for this small generator. The AVR controls the amount of current it sends to this exciter stator so that the main field is also controlled to produce the constant voltage required with a varying load.

If you can understand the above simplified description, then you need to check the cables from the main alternator phase outputs to the AVR and make sure that they are solidly connected and that any fuse in line with them is also intact. Also, you need to check the supply to the exciter stator. Then you need to check the cables from the exciter rotor to the rotating rectifiers (diodes) and from that to the main field on the rotor.

If all is OK, then check the diodes if they are OK not damaged (open circuit or short circuit ...).

At this stage, if all looks fine and sound but no voltage coming out of the main outputs, then stop the engine and get back to the rotating rectifiers plate: disconnect the two wires going to the main field. Identify the + and the - poles (look at the bridge configuration). Connect a 12V dc battery to these two wires, respecting the + & - for ~ 10 seconds only at a time. repeat after 15 sec again. (you can do this 2 or 3 times).

Reconnect the 2 wires as before. make sure all is ok connection wise and no loose items forgotten inside the alternator housing... Give it a try and see if you generate any power.

if no voltage appears ( 0Volts) on any phase to N then your AVR might be in trouble (or even the exciter windings ...?).

To check that, you can disconnect the AVR from the exciter and the main outputs. Apply a 12V dc from a battery to the wires going to the exciter field, respecting the polarities + & - While the gen-set is rotating (Secure all the output wires from the main alternator to the AVR that you disconnected!). BE CAREFUL NOT TO APPLY AT THE START - YOU MAKE A TEMPORARY CONNECTION THAT YOU CAN MANUALLY PUT ON AND OFF. Only apply the 12 Volt for short time while watching the voltage output from the main alternator so as not to exceed the voltage rating of the unit.

if you obtain a voltage (steady), even much less than the rating, then the problem will be in the AVR --> Change it.

IF ALL THE ABOVE IS PROBABLY COMPLICATED FOR YOU THEN DON't ATTEMPT TO DO ANY OF IT. SEEK HELP from a competent person. There are dangers from the electric and mechanical sides ...

I Only explained the principles to help you understand it. Be careful !

Register to Reply Good Answer (Score 5)
Member

Join Date: Nov 2010
Location: Orkney, Scotland
Posts: 6
#8
In reply to #5

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 3:24 PM

Hi and thank you.

That is a really clear explanation. It confirms my basic understanding of what I thought I was looking at. I think the message I got with this generator some years ago from the utility company, who had it as a standby, was that they had trouble starting it. I certainly had no problem starting the engine itself.

I now suspect they meant they had trouble getting it to generate because it was very seldom used (or even started), so would have lost its residual magnetism.

I will endeavout to follow your clear instructions.

Just two queries:

1. Am I right in assuming the AVR will be the bakelite box inside the alternator casing mounted on the stator of the exciter?

2. Can I test the diodes in circuit or will enough current flow elswhere to confuse the result?

I will report back in a few days and thanks again.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #8

Re: Re-energise an old Newage 250 KVA generator?

11/13/2010 8:53 PM

1) I think the bakelite box is the AVR since you said that there was some potentiometer to regulate the voltage and the gain. To make sure, there should be 2 wires going from it to the exciter field.

2) The diodes should be tested out of the circuit preferably. You can test the whole bridge (6 diodes) by disconnecting the 3 phases from the exciter and the 2 wires going to the main field. There will be One or two other components which are the Fly back diode and a surge protector (not all models have them but the Newage alternators will have them). If the brige shows a failure like a short somewhere, then disconnect these extra components and check again. They might be faulty and they will cause short circuit of the field current which will prevent the field current buildup. if your are not sure about the checking of this unit, get help from an competent electronic engineer to check it.

Register to Reply
Anonymous Poster
#11
In reply to #9

Re: Re-energise an old Newage 250 KVA generator?

11/20/2010 4:56 PM

Hi The Aggrekko plant plate said it was a Newage generator, so that was what I put in the initial heading to this query however I have discovered the generator is in fact a Dale. The 3 -phase bridge rectifier on the shaft consists of two aluminium discs with the stud diodes mounted in them. It is not easy to be sure but I do not think there are other components on these plates. I disconnected the main rotor field leads from their posts on the output side and tested from one phase input to the output side with the diode test function on a DMM. I did this for both output connection posts. As hoped, I got 480 (approx) millivolts as the reading on each (with the leads reversed for the negative side) and open circuit each time with the leads the wrong way round. From this I figured the rectifier section is OK. The field windings have a resistance of about 2 ohms measured with a DMM. I flashed the field windings with 12 volts for a few seconds twice. A lot of current initially flowed judging by the spark, but the wire did not get hot so I assume this was just inrush, then limited by the magnetism produced. I then reconnected the field wires and started the engine. Still not generating but the voltage flicking up more than before. I have looked more at the exciter. You advised the there should be two wires feeding the stator. it is a multicoil unit and it looks like the separate stationary coils are wired separately back to the control gear bits on its outside. so there are not two wires in and out but several. There are two separate "control" units one each side mounted on the stationary coils. They are different. one has a fuse (intact) and a fixed resistor and the 2 possibly trimmer screws and several wires connected in a circular pattern. the other side has a strip connector with two separate sets of wires and an adjustable rehostat. I am trying to work out if the "safety circuit" (which is not lighting up) on the main control and monitoring board reacts to the generator coming up the voltage etc of if it has to initiate that process by flashing the field through the AVR. is it possible to add photos to help this discussion? Over to you for more thoughts/suggestions please.

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#10
In reply to #5

Re: Re-energise an old Newage 250 KVA generator?

11/14/2010 5:18 AM

GA from me, great info LAA!

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Member

Join Date: Nov 2010
Location: Orkney, Scotland
Posts: 6
#12
In reply to #5

Re: Re-energise an old Newage 250 KVA generator?

11/21/2010 2:13 PM

Hi again.

I have already posted more thoughts today (attributed to "guest" as I was not logged in when I started) but here is more, corrected and updated info.

There are seven black wires that come to the "AVR" (assuming that is what it is) from the main body of the alternator. I do not know if they originate from the control panel or if some are phase wires from the main stator windings.

The AVR is in two parts, one each side of the exciter stator. There are, as you said, just two wires going into the exciter field coils, so I will be able to energise it independently. I have not yet removed the two AVR units as I need to mark up the wires first.

I have not worked out how seven wires are used unless the AVR is monitored from the control panel. Could it also have an auto flash on start up circuit in there?

I flashed the main rotor field yesterday as instructed.

I now have 25 - 30 volts across the phases at the main output of the unit. This not seen on the control panel voltmeter but is there when I put a DMM on the output connections.

I reckon this is the voltage produced by the residual magnetism I put in by flashing it. ( I had this voltage output from a 30 KVA brushed alternator (also ancient and needed flashing) before I sorted the exciting voltage section on that machine)

All this suggests that the AVR could be faulty. I would like to take it out so I can get to the exciter field wires and put DC in there as you advised.

In your post you said to mind the polarity on the DC input to the exciter field. I do not see at present how to identify which wire should be + unless I can identify the rectifier section of the AVR and hence the + output. I do not have it off the machine yet but parts of the AVR units appear to be sealed boxes so without breaking it I may not see the diodes.

It then occurred to me that it maybe does not matter which is + as the DC field coils are there to produce an AC output from the rotor and this should work either way round.

Register to Reply
Anonymous Poster
#7

Re: Re-energise an Old Newage 250 KVA Generator?

11/13/2010 12:16 PM

try to excite the inner core via a 12 volt battery

if you know how

generators tend to lose their magnetic field when stored for a long time

exciting the inner field via battery or A.V.R. usually does the trick

but check your terminals carefully

do not energise the wrong way

Register to Reply
Member

Join Date: Nov 2010
Location: Orkney, Scotland
Posts: 6
#13

Re: Re-energise an Old Newage 250 KVA Generator?

01/12/2011 3:49 PM

Just a conclusion to this thread.

I followed LAA_Lucke's advice. Flashed the rotor field, tested the diode bank, bypassed the AVR and tried a 12v input to the exciter field.

This worked so I was confident to replace the AVR.

A new AVR is now fitted and the machine is working just great.

So thanks for everyone's input and help.

Register to Reply