Load Analysis Layout

11/13/2010 1:16 PM

I have a 277/480 service with a 120/208 load in a restaraunt I am building. The a/c's (3) and vent hood are 480v. Layin lighting 277v. All other load will be gas or 120v. I understand the calculations fine, but I am not sure how to layout the written load analysis, because of the dual voltages. Can you show me a sample document that meets these critiria?

__________________
Thank you; Adam
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Load Analysis Layout

11/13/2010 1:48 PM

You are going to have 2 panels. One 277/480 panel with all of the 480 load. You will also have a 480 volt to 120/208 volt transformer to the 120/208 3 phase panel. Calculate all the the 120/208 volt load in watts to size this panel. You can then add these watts to the 480 volt panel watts to size it. Don't try to add the amps of the 208 and 480 volt loads together. Simple as that.

Register to Reply Good Answer (Score 2)
Participant

Join Date: Dec 2009
Posts: 2
#2

Re: Load Analysis Layout

11/15/2010 10:35 AM

Your question requires a little bit more analysis than just a load calculation for each panel. The calcualted loads for each panel will come into relation due to the fact that the 480/277VAC panel wil be used to feed power to the primary side of the step-down transformer. The size of the transformer will have to be able to carry the entire load calculated for the 120/208VAC panel, therefore the size of the feeder circuit for the primary size of the transformer will be affected by how much load is expected to be demanded from the secondary of it (were the 120/208VAC panel will be connected).

The total load calculations for both panels will have to be performed per the latest National Electrical Code enforced at your location. After you have performed the calculations for all your single and 3-phase loads in the 120/208VAC panel, then you will have to fine the size of transformer that will be able to supply the entire load for this panel and size the conductors and disconnect unit for the correct capacity.

Then you will need to calculate the amount of amps required to feed the primary side of the transformer (as per the transformer size you selected) and add this load to the rest of the loads that will be powered from the 480/277VAC panel.

Remeber that for 3-phase loads you will need to use the 1.73 multiplier for your voltage and once calculated, the total 3-phase load in VA will be devided equally between the three phases (this concept applies to both panels).

This is just a basic explanation, there are a lot more issues that need to be consider like AIC rating of equipment, available fault currents at all point for equipment, size of feeder conductors and distances, etc...

Register to Reply Score 1 for Good Answer
Register to Reply 2 comments