Higher Neutral Current

11/15/2010 12:11 PM

Dear All,

I took current readings on a three phase board recently and the result amazed me. I1=5.8, I2=70.8, I3=46.6 and In=30. However, using the two know formulars for calculating neutral current, I get 56.9A. Could someone explaine to me what is happening.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Higher Neutral Current

11/15/2010 1:32 PM

What were the formulas you used. The answer depends on the phase angle of the current and voltage.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: Higher Neutral Current

11/15/2010 9:24 PM

You didn't mention which formula you used. If there is any formula exists for the calculation of neutral current using the magnitudes of line currents, the formula must have sort of some assumptions such as the loads are resistive or all loads are of a certain power factor. In case, the assumptions are not valid for the loads, the formula doesn't bring the correct result. As wareagle indicated, the neutral current can be calculated using the vector sum of the line currents and in this case, you need to know both the magnitudes and angle (obtainable from load power factor) of the line currents.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Higher Neutral Current

11/15/2010 9:40 PM

This is one formula that works as long as the load PF are the same.

This gives the same 56.9 amps as in the OP.

Register to Reply Good Answer (Score 2)
Anonymous Poster
#4
In reply to #3

Re: Higher Neutral Current

11/15/2010 10:01 PM

How come the neutral current is so high,as far as i know that for 3 phase system with balanced load the neutral current must be zero ?

Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5
In reply to #4

Re: Higher Neutral Current

11/15/2010 10:35 PM

quote "How come the neutral current is so high,as far as i know that for 3 phase system with balanced load the neutral current must be zero ?"

If it were balanced all of the phase reading would be the same. Obviously it is not balanced.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#6
In reply to #5

Re: Higher Neutral Current

11/16/2010 5:55 PM

Thanks for your good answer,but why in the 4 wire cable the neutral wire is always with less diameter, i can see from this situation that neutral wire has more current than phase currents ?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7
In reply to #6

Re: Higher Neutral Current

11/16/2010 7:39 PM

Quote OP "I1=5.8, I2=70.8, I3=46.6 and In=30"

Quote Guest " i can see from this situation that neutral wire has more current than phase currents ?"

As you can see the the neutral does not carry more that the phase currents. The max neutral current would occur when 2 of the phases have no load. The neutral current then would equal to the loaded phase current. If this would happen and the neutral was too small, the neutral might be damaged. Some engineers spec a neutral the same size as the phase conductors. It has to be someones responsibility to see that the phase currents are balanced as close as possible. In the OP case, he needs to shift load from phase 2(70 amps) to phase 1(5.8 Amps). If he were to move about 30 amps to phase 1, the currents would be P1 35.8amps, P2 40.8 and P3 30 amps. Fairly close to being balanced.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); msamad (1); wareagle (4)

Previous in Forum: Megger Question   Next in Forum: Solid State Relay Used for Three Phase Resistive Loads control

Advertisement