11/20/2010 6:27 AM
How to select the circuit breaker rating ? in my project connected load is 2451KW ,maximum demand 1960KW(@ diversity of 1.25).Its based on connected load or maximum demand?
siva
Pathfinder Tags: Circuit breaker rating
India - Member - New Member
Good Answers: 164
Re: Selecting the circuit breaker rating
11/20/2010 7:26 AM
The CB needs to be selected according to the current it has to handle. You need to calculate based on kVA, not kW. Moreover, the CB is a protective device, and it must have short-circuit ratings adequate for your application.
Good Answers: 244
Re: Selecting the Circuit Breaker Rating
11/20/2010 5:39 PM
11/21/2010 2:59 AM
You have a project, connected load, maximum demand already. So there will be details of Circuit breaker also available. Better you search your college books to know How to select a fuse or breaker. Correct way of saying the diversity factor is percentage of connected load. so in this case - at 0.8.