Buchloz Relay Problem

11/20/2010 10:32 PM

50 mva ,132KV/33KV transformer of star/star yyn0 vector group . the buchloz relay is acting for external faults i.e for 33KV feeder external faults ..

__________________
rajesh
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: buchloz relay problem

11/20/2010 11:46 PM

For external fault Bucholoz relay should not operate but I think due to the heavy fault and location of the fault is near transformer Bucholoz could act falsely due to the vibrations.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: buchloz relay problem

11/21/2010 2:34 AM

i think due to havy fault in out side .oil beacaome heat up and increase its volume,so trip the transformer.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Nov 2010
Posts: 11
#3
In reply to #2

Re: buchloz relay problem

11/21/2010 1:44 PM

no,no the bucholtz will operate only if there is an issue with the trfx.a minor oil leak or significant internal winding issue will blow the bucholtz.nothing else,i should know.

Register to Reply