Kvar Loss of a Transformer

11/21/2010 2:16 PM

Pls help me to know clearly about Kvar loss of a transformer. As i know transformer itself is inductive machine. so i think it will contribute to increase Kvar.But total generated Kvar of 7 parallely connected generator is 73 kvar,that is fedded into transformer's (step up 15kv/132kv) primary & the Kvar at secondary is 59. as it is inductive machine Kvar at secondary should have had a value more than 73,i think.

but practically why it is not,rather it (Kvar) is lower in secondery than primary,pls explain me to clear my concept.

thanks in advace.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Kvar reductoin in inductive...

11/21/2010 3:10 PM

kVAR can be inductive and capacitive. In general, kVAR indicates inductive kVAR.

You mentioned "As i know transformer itself is inductive machine. So i think it will contribute to increase Kvar". It is wrong concept. The inductive machines, such as Transformer and Motors, consume inductive kVAR (though transformers are not considered as electrical loads but it requires magnetizing current and hence acts as the inductive loads). While the equipment such as generators, synchronous condensers and capacitors supply inductive kVAR.

Hope it makes sense to you now.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#2

Re: Kvar Loss of a Transformer

11/23/2010 12:02 AM

kVA = sq. root of (KVA sq. + kW sq.), this simply means that your so-called KVAR loss in your transformer is infact part of the transformer's capacity itself..you may call it as a loss since it is consuming power reactively but still this has effect on your tansformers loadability...

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3
In reply to #2

Re: Kvar Loss of a Transformer

11/23/2010 9:47 AM

rockraiden wrote: kVA = sq. root of (KVA sq. + kW sq.):

You left out an R, which might confuse someone:

kVA = sq. root of (kVAR sq. + kW sq.)

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#4
In reply to #3

Re: Kvar Loss of a Transformer

12/02/2010 9:07 PM

thanks rhk, 'twas a typo....

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply Off Topic (Score 5)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

msamad (1); rhkramer (1); rockraiden (2)