Battery Charger Using Timer

11/24/2010 7:46 AM

hi all

would you please help me on this!

i am installing automatic transfer switch controller which is controling the start and stop of the standby generator and transfer the load to the generator if the mains power failure.

the controller i fitted has no programable exercise time so the engine can run for some time and the battery is recharged, and what i am thinking is to fit battery charger controlled by timer rely and supplied from the mains power, so it will charge the battery of the genset from time to another.

on this ATS controller, when its on auto mode the mains power is present, there is one relay energized to keep the mains contactor on, so there is small load on the battery at all times.

my question is, what is the time should i program the timer of the charger so it will keep the battery voltage level, should it be ok if the chrging time is one hour per day? its 12vdc battery 90amps?

realy appreciate your advice

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: battery charger using timer

11/24/2010 8:16 AM

Normally we keep the chargeing current as low as 1A for 24x7.

Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: Battery Charger Using Timer

11/24/2010 8:41 AM

Inorder to find charging time you have to give the charging current or AH capacity of battery to find charging current.I hope 90AH is yours so in my idea 90/20=4.5A is the maximum current you can use to charge the battery it takes 20 hours to charge it.More design consideration is to be taken like internal battery resistance,conductor gauge etc. If you are not discharging the battery then daily it gets charged upto the same potential as charging.when the battery is full the charging current is zero. I hope the timer is not useful here.

Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#3

Re: Battery Charger Using Timer

11/25/2010 7:00 AM

I think you need not to make it complicated.

Normal chargers and batteries are sufficiently safe to be kept on 24/7.

I suuget to keep your system simple to minimise problems.

Have a nice day!

Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#4

Re: Battery Charger Using Timer

11/25/2010 9:12 AM

I hope your battery charger has facility to Boost Charge as well as Trlckle Charge .

If you have the battery in fully charged condition (cell voltage 2.0 v and specific Gravity of electrolite is 1200) then It has to be kept under Trickle charge.

The condition to be Checked is that the trickle current shall be set at 90ma ( Thumb rule 1 ma/AH)

It shall also be kept in mind that the cell voltage shall not exceed more than 2.15V

As it was commented in comment 2, once the trickle current is set to 90ma, it will slowly reduce to zero when the battery is charged to the set voltage and will pick up again when discharged for internal reactions. < Therefore regular Battery charge and a regular monitoring and maintenance Schedule is enough. The boost will become necessary only when the local power supply is failed for a long time ,say 8- 10 hours. On resumption of supply, the boost charge shall be carried out for 1 or 2 hours and then put it back to trickle charge.>

__________________
There is nothing either good or bad, only thinking make it so -
Reply
Anonymous Poster
#5

Re: Battery Charger Using Timer

11/25/2010 9:53 AM

Does your battery charger do not have trickle charge, 1 hour per day will not be enough to charge a 90 amps battery. You can put on trickle charge mode, so that the battery is active always.

What is the ambient temperature which you are using.

All batteries are rated for 20 deg C. you should go for 13.2 or 13.8V Battery charger for an ambient of 25 and 30 deg C.

Reply
Anonymous Poster
#7
In reply to #5

Re: Battery Charger Using Timer

11/25/2010 1:29 PM

Is there any proof that the ripples contained in the full wave rectified voltage useful for the battery to reduce sulphation build up ?

Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#8
In reply to #7

Re: Battery Charger Using Timer

11/25/2010 4:04 PM

All batteries are considered as Infinite capacity-capacitors. There are no ripples when on charge, whether 1/2 wave, full wave, 6/12 pulse rectifiers.

Reply
Commentator

Join Date: Jan 2008
Location: Kitchener, Ontario, Canada
Posts: 62
#6

Re: Battery Charger Using Timer

11/25/2010 1:27 PM

http://www.cirkits.com/spc3/

have a look you can convert this to turn on the charger when the battery gets to a set point and turn off when done use a relay to drive it off and on simply and easy