Voltage Drop Calculation

11/25/2010 12:04 AM

I have a question regarding to captioned. I am doing a project for Electrical Service Board Extension and connect the power cable to MCCB and MCB from it. Then, the cables will be connected to the power socket. I am wondering if the voltage drop calculation has to be calculated for the whole path from Service board to sockets or just the separated segments from MCB to sockets. Please help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Voltage Drop Calculation

11/25/2010 1:56 AM

Without a load, there will not be a voltage drop. You should remember that from electricity 101.

The minimum wire gauge that you should use is set by your local building standards. The default standard for most wiring in the USA is NFPA70. I recommend that you attend a seminar on how to use this standard because it is a confusing standard. The confusion comes from the vast number of scenarios and exceptions that the standard covers.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: Nov 2010
Posts: 4
#2
In reply to #1

Re: Voltage Drop Calculation

11/25/2010 3:04 AM

Thanks for your reply. In fact, the power sockets that we are using are 63amps. I got confused on how to calculate the voltage drop in different segment. The connection sequence is from MCC to MCCB and connected to power socket finally. I have calculated the wire gauge from MCC to MCCB and then MCCB to sockets. However, one of my colleague said that I should calculate the volt drop from MCC all the way to sockets in order to determine the wire gauge. I'm totally confused.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Voltage Drop Calculation

11/25/2010 10:12 AM

The voltage drop of the individual cable segment should be within 3%, while the total voltage drop (for both feeders and branch circuits) from the power source (generally transformer secondary bus or main power panel etc.) to the load should be 5%.

See NEC 210.19(A), FPN 4 and 215.2(A)(3) FRN 2.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#4

Re: Voltage Drop Calculation

11/26/2010 12:45 AM

MSAMAD got one part correct which is the 5% total voltage drop from source to load and the 3 % from branch (MCC) to load. The second part is to calculate what is the voltage drop that will occur with the assessment of the conductor you select for the load. Remember to identify if the load is continuous and if yes, multiply your current (amps) rating by 1.25%, then; if single phase, the formula to apply is ( 2 x length of conductor x resistance of conductor x Amps divided by 1000) this will equal your voltage drop with the selection you made on the conductor. The preferred method is to apply the following formula ( (2 if single phase or 1.73 if 3 phase) x L x (12.9 if copper 0r 21.2 if alum) x amps divided by the percent voltage drop (either 5 percent of supply or 3% of branch) This formula will give you the size of the conductor to use for this load. If this process is still unfamiliar, then suggest you get licensed electrician to assist with table 310.16 and table 8 of NEC/NFPA70.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Voltage Drop Calculation

11/26/2010 11:30 PM

Just to clarify:

For voltage drop calculation, use 100% current, not 125% (125% is used for cable ampacity and breaker sizing in NEC). For the voltage drop calculation formula see this: http://cr4.globalspec.com/comment/535743/Re-voltage-drop

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#6

Re: Voltage Drop Calculation

11/27/2010 12:40 AM

normally the size of cable determined based on the load capacity as well as the short circuit rating of the system.

so you may consider the length from service board to socket.

please note that the selected cable should withstand the shortcircuit current for a specified period of time.

Register to Reply