How do you use a thermistor and a voltage analog input module to gather a temperature reading for use in a PLC? It can be done, right?

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Pathfinder Tags: analog inputs thermister
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#1

Re: PLC Thermistor Input

11/29/2010 11:08 AM

Of course! There are at least four possible approaches, maybe more:

  • Get a temperature transmitter that uses a thermistor as the temperature sensor and converts the temperature to a 4-20 ma. loop signal, then use a PLC input board that accepts a 4-20 ma. signal.
  • Similar to the above, but put a resistor in the loop and input the voltage across the resistor to the PLC analog input. (Choose the resistor to match the voltage range of the PLC analog input.)
  • Maybe the PLC manufacturer makes an input board/module specifically for thermistors?
  • Create a circuit with a power supply feeding the thermistor. Then input the voltage across the thermistor to the input of the PLC. (You'll need to choose the power supply considering the resistance range of the thermistor and the voltage range of the analog input.)

In all cases, pay careful attention to things like grounding, polarity, power dissipation, safety (including any requirements for intrinsic safety (or explosion proofing)), ...

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: May 2010
Posts: 11
#2

Re: PLC Thermistor Input

11/29/2010 11:51 PM

Here is a dual Thermistor converter. They are around $225. Datexel DAT4532C. you can find them on www.datexelusa.com.

Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 22
Good Answers: 1
#3

Re: PLC Thermistor Input

11/30/2010 10:34 AM

PLC has power supply and main brain and several attached PLC input and output cards. Most output cards are digital on/off cards. Some are analog output cards which require calibration with the potentiometer on the card and some PLC programming that sets output registers to zero and span. PLC input cards can be digitial input to monitor on/off conditions of solenoids or switches and PLC input cards can be analog inputs. These cards are not calibrated rarely unless special card.

Inputs of analog cards range in precision from 8 bits, 16 bits, 32 bits, 64 bits, etc.

The higher the precision the greater the cost.

To get an analog input into a PLC card, you can input current, voltage or other depending on type of card and precision of card.

Once range and type is selected, you need PLC programming knowledge to program PLC analog input.

PLC analog input card either accepts variable range 4-20mA current input or 1-5 voltage input or 1-10 voltage input. PLC program register uses analog register to store information. Transfer analog register value into storage register. Transfer storage register value to comparator register or math register to perform calculation.

PLC programming is required.

For Example in modbus Ladder Logic ProWorX uses 3X analog register to store value. Additionally value can be defined in 8 bits, 16 bits, or 32 or 64 or 128 bits depending on how expensive a PLC you are using. Generally cheapest PLC's are used.

8 bits was common, then 16 bits. You will find many 16 and 32 bits out there.

Once 3X register stores value, perform block transfer to 4X register.

Once this is done, you just take that stored value and insert it into some math register to add it to something or perform some mathematical comparison with another value.

From there to transfer the result to Scada. Place final result in another 4X register and specify that 4X register in the Scada machine database. You will need to construct a register map in your PLC. With this map you can specify which registers you want to transfer information from your PLC to your Scada database. Generally the database includes fields and tags. Once you do this, in your Scada software you can link the fields and tags via a GUI (graphic user interface) to an operator screen that the operator can push buttons or slides with pictures of your process.

Different Vendors have different strategies and schemes to get analog information into their PLC's using their programming. GE has their own scheme, Schneider Electric has one, Allen Bradley, Crouzet, and many others each have their own PLC languages.

Concept is a popular one, ProWorX is also used. Generally in real life only engineers are allowed to do this. Technicians are allowed to do some stuff but more and more ITS takes over so technicians are left with installation and field calibration. Calling them potentiometer tweakers. Electricians sometimes do this work as well depending.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2012
Posts: 3
#6
In reply to #3

Re: PLC Thermistor Input

11/17/2012 5:47 PM
Register to Reply
Member

Join Date: Dec 2010
Location: Los Angeles
Posts: 9
#4

Re: PLC Thermistor Input

12/30/2010 6:58 PM

An economical way to get several thermistor inputs is to use a multiplexed input module, with a common interface such as Modbus RTU. An example is http://www.icpdas-usa.com/products.php?PID=494 . It has six channels wich comes to $70/channel at the price of $419.

Register to Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#5
In reply to #4

Re: PLC Thermistor Input

12/30/2010 8:09 PM

Thank you for posting this. It is good information!

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Coldspot (1); Gizmo787 (1); rhkramer (1); serkan (1); SUMPI (1); TechEric (1)

Previous in Forum: Gauge Calibration   Next in Forum: Beam Angle of RADAR Type Level Transmitters

Advertisement