Please someone tell me the Standard Temprature correction factor of winding insulation resistance of 3X150MVA,500/220KV auto transformer,in the light of international standard.As well as the minimum acceptance limits and calculations. Thanks and best regards.
Re: Standard Temprature Correction Factor of Winding Insulation Resistance
11/30/2010 11:09 PM
Formula for temperature correction:
R40 = K x Rt
Where R40 is the insulation resistance Mega Ohm corrected to 40 deg C.
Rt is the measured resistance at actual site temperature
K = 10 (0.0301 t - 1.2041)
This means roughly a resistance re-doubling at every 10 deg C of decreased temperature and vice versa.
Knowledge sharing is a WIN-WIN situation
12/06/2010 1:34 PM
hi ,i am graetful to you that you guide me in this matter,kindly guide me about the formula for calculating the minimum insulation resistance of T/F wdgs at 15sec,60sec or 600sec.once again i am thankful to you.best regards.Engr.Asim
11/30/2010 11:27 PM
For transformers rated 110 Kv and above 60 seconds insulation resistance in mega - ohm is 240 for a winding temperature of 40 deg C.
Please note that yo have to carry out polarization index (PI) test which is a ratio between IR values for time intervals 1:10