Field Failure Relay with and w/o Under Voltage

12/05/2010 10:37 PM

What is purpose of providing two different filed failure protection in generator with and without under voltage ?

Register to Reply
Pathfinder Tags: field failure relay
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Filed Failure Relay with and w/o Under Voltage

12/06/2010 6:19 AM

Do you mean field failure protection?...To protect from the thermal damage due to sudden loss of excitation.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Filed Failure Relay with and w/o Under Voltage

12/06/2010 10:53 AM

This prevents the generator documentation from being incorrectly filed. Unfortunately most of these relays work very poorly. Anyone who has ever looked for generator documentation knows this.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Filed Failure Relay with and w/o Under Voltage

12/06/2010 6:24 PM

I think you mean to say you have a generator with two rotor field failure relays, one of which is only armed (active) when the generator terminal voltage is below normal, the other is active always. You do not mean you have different field failure system for a generator with output under-voltage protection compared to a generator without output under-voltage protection!! The reason, I think, would be that any good excitation scheme will increase excitation to several times rated for as long as possible after a short circuit. This ensures the short circuit current due to a load fault is kept high so that the fuse or circuit breaker feeding the faulty part of the load opens quickly. You will realise that a fuse breaks much faster if current is many times its rating than if it is only say 1.5 times. The field-fail relay operating ONLY at low generator terminal (output) voltage would have a higher current setting because a healthy excitation system ought to give higher [above rated-current] field current under these conditions. A short-circuit or severe overload always pulls generator output voltage below normal.

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 20
#4
In reply to #3

Re: Filed Failure Relay with and w/o Under Voltage

12/06/2010 9:59 PM

Two different relay for field failure one is with under voltage second is without under voltage . what is field failure without under voltage ?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #4

Re: Filed Failure Relay with and w/o Under Voltage

12/07/2010 6:31 AM

"No field voltage" or "no field current" is easy to detect (when the field is connected by slip-rings or if an exciter field is monitored), but a better field failure relay will identify that field current is not as high as it should be. Field current is more likely to be too low or high because the voltage regulator/excitation system has a problem than because the field windings have failed. If the field strength is too low, a generator in parallel with other generators will work at a leading power factor and can lose synchronism and "pole slip". If you mean undervoltage at the main generator output terminals, this may not happen with weak field because parallel generators or the Grid keep the voltage up to normal at these terminals.

Register to Reply
2
Anonymous Poster
#5
In reply to #3

Re: Filed Failure Relay with and w/o Under Voltage

12/07/2010 1:26 AM

Generally the main field fail relay is in the circuit of excitation current from static exciter(AVR) to field of generator or rotary exciter field and whenever there is any discontinuity of field current to field from static exciter or AVR, this relay will operate and trips the breaker & AVR. This is most essential when two generators are running in parallel. To protect the field failed generator, this relay is essential otherwise other generator will supply the second generator and second will run as motor and heavy circulating current will flow which will damage the second generator. This Field fail relay is without U/V and current operated. During this parallel operation as supply from other side is available at generator terminal, U/V will not operate and only protection in this case is Field fail relay and then reverse power relay. When generator will run in islanding mode, U/V will also operate during field failure as generator will not be able to build up the voltage.

Register to Reply Good Answer (Score 2)
Anonymous Poster
#7

Re: Field Failure Relay with and w/o Under Voltage

12/07/2010 8:48 PM

i don't think you guys grasp the original question. i think the question originates from the setting of a field failure relay on some multifunction generator protection relays that have an added feature which activates the field failure only if the voltage drops below a selected threshold. Or one can elect to enable the field failure relay solely on the generator mho characteristic i.e. the generator impedance as seen by the system.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Field Failure Relay with and w/o Under Voltage

12/07/2010 9:53 PM

You might be right. I'm sure the documentation that was filed away would explain how to use these relays.

__________________
"Don't disturb my circles." translation of Archimedes last words