Ground Resistor for Generators

12/15/2010 10:14 PM

Hi guys....We want select a grounding resistor for a generators of 1200 Kw, 460 voltios. There two equal generators parallel operation. Can give me somebody a guide for select the resistors?..

Register to Reply
Pathfinder Tags: Grounding resistor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Ground Resistor for Generators

12/15/2010 10:32 PM

No idea about 460 voltios generator. A grounding resistor for two generators?? You want somebody as a guide for selecting resistors?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Ground Resistor for Generators

12/16/2010 6:51 AM

What is the desired ground fault current?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Ground Resistor for Generators

12/16/2010 11:10 AM

TAKE CARE!! IF you get told a resistance which limits current to less than minimum to operate "ground fault protection" you will just get a melted grounding resistor and still have an earth fault!! Are we talking a "3 terminal" generator or a "4 terminal" generator?? It has an effect on how you can earth.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Ground Resistor for Generators

12/16/2010 11:08 PM

BEFORE YOUR QUESTION IS ANSWERED

TWO GENERATORS ARE RUNNING IN PARALLEL .

IF BOTH THE GENERATORS ARE SYNCHRONISED IN THE SAME BUS DIRECTLY WITHOUT A GENERATOR TRANSFORMER .

IN THAT CASE ONLY ONE GENERATOR NEUTRAL IS SUPPOSED TO BE GROUNDED (FOR PROPER SHARING OF REACTIVE KVAR).

IN THIS RANGE GENERATOR NEUTRAL SHOULD BE GROUNDED THROUGH A HIGH IMPEDANCE GROUNDING THROUGH NGT .

THE SECONDARY WINDING OUTPUT OF NGT SHALL BE USED FORV 59G PTROTECTION.

THE NGT RATING FOR EACH GENERATOR SHOULD BE 270 VOLT-14KVA.

THE SECONDARY OUTPUT SHOULD BE MAX-60VOLT(THIS SHOULD BE ADJUSTABLE ACROOS A VARIABLE RESISTANCE)

THE NGT OTHER END SHOULD BE CONNECTED THROUGH A KNIFE SWITCH TO A DEDICATED TREATED EARTHPIT.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#5

Re: Ground Resistor for Generators

12/17/2010 12:03 AM

I never heard of such resistors. your question is confusing. Have you done any homework before posting this Q? if yes details please!

__________________
Subramanyam
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Ground Resistor for Generators

12/17/2010 4:54 AM

Post #4 from Guest is good (For 4 terminal generator with neutral). But, if you have only one ground resistor, the NGT (Neutral Grounding Transformer) must be switched by contactor or manual changeover switch to neutral of running generator (You may operate with only one generator on-line). Or else, if you have NGT on each generator neutral, only one must be connected in normal operation.

Register to Reply
Anonymous Poster
#7

Re: Ground Resistor for Generators

12/17/2010 6:28 AM

Generator neutral is grounded through an impedance to limit the fault current. This fault current is also used for tripping the set where an overcurrent relay is used. Generally the neutral is grounded through a distribution transformer secondary of which is loaded through a resistor and a current coil of the earth fault relay. Transformer is used so that a low value resistance may be used which offer higher impedance on primary side to limit the fault current. The value of resistor is chosen based on the principle that power loss in resistor is equal to the capacitive charging VA of the generator. So to design the grounding resistor value of generator, connecting cables (or bus duct etc.) would have to be considered. The resistor is rated for short time power dissipation.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (3); electricalexpert65 (1); kvsubramanyam (1)

Previous in Forum: Would More Ground Rods Help?   Next in Forum: Reacceleration Schemes LV Motors

Advertisement