Anonymous Poster

Earthing While Working on Dead OHL

12/18/2010 7:06 AM

if i am working as a lineman in an overhead line and my supervisor request me to make maintenance on the line 33kv . and in the site argument happen between technicians where to put the earthing for safety

is it towards the source or towards the load or anywhere?

can any one expain the situation from engineering point of view

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Anonymous Poster
#1

Re: earthing while working on dead OHL

12/18/2010 7:09 AM

Read your company maintenance procedure for the Job. better do not take any suggestion from here. It is your life.

Reply Good Answer (Score 2)
Anonymous Poster
#2
In reply to #1

Re: earthing while working on dead OHL

12/18/2010 7:15 AM

i forget to mention that the line is off

Reply
4
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: earthing while working on dead OHL

12/18/2010 7:27 AM

The circuit should be earthed at both ends of the line. Also at a point as near to the work area as possible (ground spike and line clamps).

If the work involves breaking the continuity of the line then two sets of line clamps should be used, again as close to and each side of the work area. With two sets of line clamps they should be connected to a common earth spike.

The reason for close proximity earthing is the danger of lightning strikes on the line. If the weather turns and there is a possibility of lightning then all work should be suspended.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 4)
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#11
In reply to #3

Re: earthing while working on dead OHL

12/19/2010 3:44 AM

TonyS is right here. I'd like to add, if you are not qualified to perform HV work you are better not touching it.

The terminology we use to describe what TonyS is telling you are Proving Earths and Working Earths. To isolate for electrical access takes a well worked out switching sheet and access permit. There is no room for argument and if arguments are ensuing then don't sign on the access permit and definitely don't touch.

The hardest thing can be identifying all the "Sneak Sources" such as Voltage transformers and the items mentioned by other posters.

Radial feeders are not too diffucult but if the circuit is ring fed, then more than one Proving Earth will be needed to protect from each direction of supply. Your working earth needs to be close to you and must be visible. For ring fed circuits you need to be working between two working earths. Obviously all earths and isolation points must be accounted for in the switching sheet.

I can't speak for other juristictions but where I work one person alone cannot devise and authorise the switching sheet and perform the switching. It takes a minimum of two qualified people to sign off before any switching can commence and the switching officer must have a qualified Safety Observer watching the procedure. The preference is for prewritten fully risk assessed switching sheets which are reviewed against the schematic at each use unless the work is proven routine.

I have done a lot of HV work but am as wary as all hell when performing any of the tasks I'm qualified for and therefore discuss with my colleagues to ensure no errors creep in.

Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#18
In reply to #11

Re: earthing while working on dead OHL

12/19/2010 10:20 AM

Further to the above two posts: If you have not been trained - worry! I suspect that you work in a less formal environment? If your company does not have a formal switching and isolation and earthing procedure for work on transmission lines, try and get something started, even if it is via your safety office or engineering head office. You don't have to go first world with everything, but you only have one life and this is one instance where very formal systems are essential. It does not have to be complicated, just formal. The system should make that you and the supervisor come to the same answers independently, removing room for arguments.

Anyway, from an energy supply point of view, you ALWAYS work between earths, preferably visible earths:

  1. You may think of a "source", but you may not know where all the sources are. You don't know what your clients are doing!
  2. As the others stated, lightning can be an unwelcome surprise, and you may not even know about the strike a few kilometers away.
  3. If there are other power lines in close vicinity, they may cause induced currents in your lines.
  4. Once our utility's 22kV power wires fell over our wires, but my linesmen was OK, because he put up the earth connection very close. He was therefore not injured, even though he could see the earth wire "snaking" due to the short circuit current.
Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#21
In reply to #3

Re: earthing while working on dead OHL

12/22/2010 4:17 AM

Switched earths should be as near as possible to the work position along the line. Working earths,weither to a mat or stake should be within sight of the work area.

__________________
I attend work so my dogs can have the good life.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Earthing While Working on Dead OHL

12/18/2010 9:12 AM

Guest and Tony here have the correct ideas. You must follow your job specified safety procedures because many people will be relying on how your safety controls are configured. If your safety controls permit more than one ground connection (I suspect they do) then a safety ground upstream and downstream of your work line will maintain a ground on both sides of your line if the cable becomes disconnected.

But don't get in the habit of analyzing your safety rules and regulations. Sometimes the rules are made for your safety, sometimes they're for somebody else's safety (rescue worker, colleagues). The rules did not come from people just engineering what they want to happen. They came from analyzing mishaps that people did not anticipate. Safety rules are not flawless, but modifying them casually in the field is a recipe for disaster.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#5

Re: Earthing While Working on Dead OHL

12/18/2010 11:47 AM

In addition to TonyS's response, make sure the protective grounding clamps and cables are rated as safety grounding assemblies. Conventional tap clamps are not safety grounding clamps nor are they rated as such.

I don't know your location but in the U.S. safety grounding and standards are the responsibility of the IEEE/ ESMOL Subcommittee (Electrical Safety & Maintenance of Overhead Lines) and IEEE Standard 1048 covers Protective Grounding. You might take a look at www.ieee-esmol.org. Protective grounding is also covered in ANSI C2 (National Electrical Safety Code). Comparable IEC and standards of other countries also exist.

Reply Score 1 for Good Answer
Anonymous Poster
#6

Re: Earthing While Working on Dead OHL

12/18/2010 12:02 PM

CR4 Admin: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Anonymous Poster
#7

Re: Earthing While Working on Dead OHL

12/18/2010 11:21 PM

toward the source. the voltage will not get to you if the grounding is between you and the source. also you should as a safety precaution ground after you to the load. there might be a switch that some one pulls on so grounding on both sides is best.

Jonathan Schultz

Schultz Electric

Reply
Associate
Peru - Member - New Member India - Member - New Member

Join Date: Feb 2007
Posts: 31
#8

Re: Earthing While Working on Dead OHL

12/18/2010 11:36 PM

Dear it is sure towards SOURCE. Putting it towards load will not affect much because the "final outcome of damage" is very slow than the speed of electricity! But it is general safe practice to put earthing or shorting towards source while working on OH lines for maintenance.

__________________
Workflow
Reply
Anonymous Poster
#9

Re: Earthing While Working on Dead OHL

12/18/2010 11:56 PM

CR4 Admin: Deleted Post

Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.

Reply Off Topic (Score 5)
3
Anonymous Poster
#10

Re: Earthing While Working on Dead OHL

12/19/2010 2:05 AM

The lines are, normally, shorted phase to phase. If the line is energized, accidentally or on purpose, the short circuit will pull the the line breakers open. An accidental power-up is usually accomplished by someone's standby generator. Unless you know where these generators are located, you cannot short to the source. Connecting the phases together will over load the standby generator. Connecting the phase short to earth may provide further protection. The grounding rod must be, at least 10 feet (3.3 meters) long, driven full legth into the ground.

Become familiar with IEEE Standard 1048 and your company's safety procedures.

When working with primary power, there is no such thing a a "off" line.

Lightning strikes are a possibilty. A new wrinkle is solar power.

Last of all, there are bold HV electricians and old HV electricians; however, very few old, bold electricians, HV or otherwise.

Reply Good Answer (Score 3)
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12

Re: Earthing While Working on Dead OHL

12/19/2010 4:35 AM

Hi

if you are asking this question I wonder do you/your company have a safety officer/safe working procedures/safety training?

I find this a dangerous question and scary that you have come to this forum to ASK complete strangers for advice on high line safety.

If you are NOT sure of the safety protocols... then WALK AWAY.

Without the benefit of actually being there.... it sounds to me that you got problems, and as you've stated there has been a "Site argument"... it would seem there are no real bosses, no real safety procedures and no-one really knows what they are doing.

Not an enviable situation!

__________________
The square root of nothing is what you make it!
Reply Good Answer (Score 2)
Anonymous Poster
#13

Re: Earthing While Working on Dead OHL

12/19/2010 6:24 AM

Do you heard about Earth switch???........Oh..have you seen HV switchgear?

Reply
Anonymous Poster
#14
In reply to #13

Re: Earthing While Working on Dead OHL

12/19/2010 8:03 AM

Have you worked on it? If not keep quiet!

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15
In reply to #14

Re: Earthing While Working on Dead OHL

12/19/2010 8:07 AM

in reply to 13 & 14.. while your posts maybe valid.. is there any need to put in print what we already know?

__________________
The square root of nothing is what you make it!
Reply Off Topic (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#16
In reply to #15

Re: Earthing While Working on Dead OHL

12/19/2010 8:21 AM

I've voted a GA for that.
Our friend Guest is getting to be a total pain, I've reported several of his posts but the moderators must be asleep.

__________________
The reports of my death are greatly exaggerated.
Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#17

Re: Earthing While Working on Dead OHL

12/19/2010 9:37 AM

Any ground and/or short circuit jumpers should be on the supply side. if on the load side you lose your protection when you open the line. P.S. Install them on both sides. There is always some clown who will start up a generator without a transfer switch. Although illegal, some home owner kills 3-4 linemen every year. Don't let it be you! P.P.S. Since you asked the question, I applaud your concern for safety but seriously question the company's knowlege of, and training in safety protocols. Good luck and I hope I don't read about your death in the newspaper. SAFETY IS EVERY-ONE'S RESPONSIBILITY!!!

Reply
Anonymous Poster
#19

Re: Earthing While Working on Dead OHL

12/19/2010 10:12 PM

if you're a journey lineman, you already know what to do.

Reply
Active Contributor

Join Date: Nov 2010
Posts: 16
#20

Re: Earthing While Working on Dead OHL

12/21/2010 3:00 PM

Ok, I am a self studied layman but I'd like to put it out there to see if I am right. My thoughts: The flow of electrons follows the easiest path. The flow will not go against itself, like putting two positive leads together. If you are not grounding to ground (neutral) which links to the earth from what I know, then the most logical place to ground to would be the load side which theoretically accept the flow of electrons should something go wrong. One electrician I had discussions with equated electricity to the flow of water. If it is this simple, the above makes sense.

I bear no responsibility for the above theory. I don't want anyone to be killed. Be careful boys. I have a lot of respect for you guys. Scary and dangerous stuff.

Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#22
In reply to #20

Re: Earthing While Working on Dead OHL

12/26/2010 7:17 AM

NO!

Every conductor has resistance. MASSIVE fault current flowing past your access point raises the voltage at your access point which causes current to flow through you because you are only a resistor ( a dead or injured one to be sure, but just a resistor).

Any current above about 30 Milliamps through your body will kill you, end of story.

Portable earths in a 3 phase system firstly short the phases together (to operate the protection) and then via a cable suitably sized for the fault current bonds the system to the ground network. The ground is necessary in the common case that all three phases don't trip simultaneously. Take the case of fuses, typically only 2 actually blow in a 3 phase event which does not also have the extra return path provided by the earth / ground conductor. If the HV system connectioin to ground is not present the remaining live conductor will be held at ground potential preventing rise of voltage at any point after it in the circuit.

In a single phase earth return system the ground is the only protection.

I reiterate, High Voltage is a specialised field.

Now to the water analogy. Say you have water from a piston pump designed to power a water blaster that puts out 50,000PSI at 200 litres (55US Gals, 44 IMP Gals) per minute but capable in a fault of producing 5000 litres per minute, yet the delivery hose is designed for the 200 liter flow. Imagine you have opened the end of the hose by removing the nozzle and then the system starts delivering 5000 litres while you are working at the start of the hose. The pressure drop along the hose will assure that you suffer high pressure at your (line side ) end (try it with a garden hose, as you will know a leak at the tap still occurs even when you are flowing water through the hose at full bore).

Hope that helps, I realise you are interested rather than shooting off, but the consequences of getting it wrong are deadly.

Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#23

Re: Earthing While Working on Dead OHL

12/26/2010 7:30 AM

Something all of us who are actually high voltage qualified should have noted earlier is a HV cable is not "Dead" unless it is proven de-energised and earthed. This is the proving earth and it is ALWAYS at the point of supply.

What may help you is some knowledge of those who post trying to help.

Some comment on everything regardless of actual knowledge others try to only comment in actual fields of expertise. I am one of the latter and I have 37 years experience in the Electrical Game. A couple of other posters to this thread clearly have similar experience.

The way to sort out the former is look at the amount of time subscribed to CR4 and the amount of posts placed. Some posters manage over 2000 posts in 6 months on every topic know to man, would you want to entrust your safety to such a person?

Reply
Anonymous Poster
#24
In reply to #23

Re: Earthing While Working on Dead OHL

12/26/2010 5:49 PM

"The way to sort out the former is look at the amount of time subscribed to CR4 and the amount of posts placed"

So how does Guest with 3 GA's fit in this scheme?

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#25
In reply to #24

Re: Earthing While Working on Dead OHL

12/26/2010 6:12 PM

You don't. Silly Rabbit... If you wish to claim credit for your insight, come out of the shadows with at least a moniker.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Anonymous Poster
#26
In reply to #25

Re: Earthing While Working on Dead OHL

12/26/2010 6:57 PM

Interesting leap to kudos, when the question asked is about the surety of the method of evaluation proposed.

What if the OP applied that 'formula' to say the person/knowledge behind MoronicBumble or say TonyS in a few months time?

Reply
Reply to Forum Thread 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!