Generator Reactive Power at Minus Values

12/22/2010 1:43 PM

We have 12 gas engines and all they are adjointed with AVK generators. 12 engines are divided to 2 groups by 6. These seperated into 2 group machines are connected to one Step-up transformer. One of our engine has got a problem during the start of engine. When we give the start, we usually see the engine's reactive power at "– values" i.e. starts with ~ -25kVar and goes until ~ -2000kVar. Although its reactive power increases in negative way, it produces Active Power at normal rates. We saw if we wait and nothing to do, reactive power goes until -2000kVar after that it gets normal and we see positive and normal reactive power values. And there is also one thing we saw, when we give start and when we see the reactive power goes at minus values, we push the stop button and we wait a moment then again we give start. Consequently, reactive power which is in minus values, it suddenly turns to positive. Why does this happen? Is there anybody who deals with a problem like this before? Thank you for your commenst from now on.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Generator Reactive Power at Minus Values

12/22/2010 2:01 PM

Because of minus temperature in europe now.

Reply Score 2 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Generator Reactive Power at Minus Values

12/22/2010 2:45 PM

You did not give generator rating. Not possible to know if -2000 kVA is big % of rating. You did not write how long to go -25 to -2000 kVA or -2000 to normal, such information helps. A generator will always go into -ve (leading current) reactive power as engine throttle is opened - unless generator excitation (field current) is increased. Usually, an automatic circuit raises the excitation as the set loads-up - on multiple parallel sets a "Busbar Voltage Control and Reactive Power Sharing" system is commonly used. When a set is stopped, it is often switched to "voltage regulator/AVR" "power factor" control while it is unloading (this ensures that both reactive and active power are reduced to small values before main breaker to busbar is opened - consequently, breaker opens at low current), if stop is cancelled power sharing is reconnected. "...suddenly turns to positive" suggests a fault like a failing relay/contact exists in circuits from stop or start/run or "breaker closed" relays to generator AVR. Not knowing particular model of set or make and type of AVR makes it difficult for other posts, who may have experience of them, to help.

Reply
Member

Join Date: Dec 2010
Posts: 5
#5
In reply to #2

Re: Generator Reactive Power at Minus Values

12/24/2010 1:36 AM

Generator's rating is 8.73 MW it happens during the start the engine. When it synchronaizes with the grid it starts to absorb reactive power and we see on the digital and and analog meters - values. we see -25, -100, -250 .... -1000, -1250 kVars in a 5 -7 minutes until it goes to -2000 kVar. when it gets -2000 kVars.By the way I know the generators absorbs reactive power during the first start but very few times and it is momentary and takes just seconds. And we check all the wires, relays, cables everything even on the generator. we retightend them all as well but the problem is still exist. AVR's model is ABB Unitrol 1000-15

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Generator Reactive Power at Minus Values

12/24/2010 7:08 AM

Unitrol 1000-15 seems quite complex and little can be done with it without reading manual!! Simple suggestion is to exchange a 1000-15 from a good machine with that on your problem machine. If problem moves with AVR, then trouble is in AVR (could be software settings, not hardware). If problem stays on problem machine, it is not AVR but the external instructions during start up or a defective input signal. Have you checked that the input signals to the AVR are not fluctuating during period of "wrong" kVAr?? That could indicate a heat or current sensitive fault in external CT/PT/transducer. Is there a facility to manually control voltage during loading - if one can load-up kVAr smoothly in manual, this points to trouble with automatic path?? The basic problem is that the machine voltage is not being raised after connection to bus. Is the AVR or overall control giving error messages like "excitation limiter" operating??

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Generator Reactive Power at Minus Values

12/22/2010 2:53 PM

Is this a new installation, or has it been in operation longer time? If existing, has it always done this, or did it just start happening recently?

On what are you reading the kVAR - a panel meter, or other instrument? Analog or digital meter? Where is the source of the meter currents and voltages? Maybe something is mis-wired to that meter, or there is some damage somewhere that is affecting its input. Physically trace its wiring from the CTs and PTs, and compare it to one of the gens whose meter reads normally. You have 11 other ones that are correct - you should be able to find the difference.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Member

Join Date: Dec 2010
Posts: 5
#7
In reply to #3

Re: Generator Reactive Power at Minus Values

12/27/2010 10:43 AM

it has just started to do this for 2 months we didn't have this kind of problem before. we see the reactive power both analog meter and on the PC at minus values. we did all inspections with the wires,relays etc. but the problem is still same. we read in the first start around - 50,-60 kVAR then it goes to -2000kVAR in five mins, but active power is at normal values just the reactive power value goes to -1500 - -2000kVar when it sees -2000 kVar the reactive power turns to the normal positive values i.e. 1860 kVa, 1950 kVar etc. during the operation

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #7

Re: Generator Reactive Power at Minus Values

12/27/2010 11:11 AM

Post #6 suggested swapping the Unitrol on problem unit with that on a good unit (with a spare Unitrol). Did you do this?? Thinking further, I guess AVR control could have 3 phases 1) Voltage control for synchronising 2) Power factor control for Loading-up 3) Load (KVAr) Sharing Control when unit is loading. It is possible command 2) to Unitrol on serial link from Master Control is corrupted, Unitrol ignores it, stays in voltage control, unit progresses into leading VArs as MW increase. When command 3) comes the annomally is corrected. Try re-loading software on problem unit.

Reply
Member

Join Date: Dec 2010
Posts: 5
#11
In reply to #9

Re: Generator Reactive Power at Minus Values

12/29/2010 1:33 AM

I think I m goona swap one of the well Unitrol with this. If I don t get any result, I m gonna dense on software issue. I ll share the results, thank you

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #7

Re: Generator Reactive Power at Minus Values

12/27/2010 12:06 PM

Further to post #9. It is possible that set-points, like power factor, are entered into the Unitrol AVR. It should be possible to view them via the Unitrol key pad on problem unit. Then compare values got same way from a good unit. In any case, -2000 KVAr with 9000 kW unit is 0.98 power factor [leading], not a problem - but it is a possible value with a setting of unity [ 1.0 ] power factor.

Reply
Member

Join Date: Dec 2010
Posts: 5
#12
In reply to #10

Re: Generator Reactive Power at Minus Values

12/30/2010 2:16 AM

Today we had a new experince with this machine. When we gave the start it absorbs reactive power and stucks at -2000kVar and active power was 2700 kW.After a while machine tripped and gives fault messages as "Generator Protection underexcitation Q<Trip" and "Generator breaker trip circuit indication" after these breaker is opened.Then we resarted it again. We measured all output signals of the Unitrol with changing the pf values. Everything seems OK(during the machine at normal operation, reactive power at positive values). I read the Unitrol Manual, there is an Kq which is reactive current influence , it has a setting range between -20 to +20, it is set +3 in the AVR. Does it make any sense if we play with this number via increasing or decreasing?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13
In reply to #12

Re: Generator Reactive Power at Minus Values

01/01/2011 6:26 AM

I wrote in post #10 that you must compare AVR parameter value on your problem unit with that on "well" unit. If value is same on "well" unit, there is no benefit from changing - all you do is risk adding to trouble or making a new one to confuse diagnosis. You report you now get "underexcitation" trips - the fault is getting worse. I suggest you swap the problem AVR, after recording its parameter settings and those of "well" unit. Are settings in "Commissioning Report" or "Schedule of Settings"?? If not, best to record what you have BEFORE any change. I tried to find Unitrol manual on BBC website, but only found "sales" brochures, which give poor information. I can only guess it is a "loop" stability parameter, bad idea to change. If you could point me to manual on web, I will try to help - but I think you must now change AVR to make progress!!! Going now, New Year's Day music concert from Vienna [TV] calls!

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #12

Re: Generator Reactive Power at Minus Values

01/02/2011 3:24 PM

Further thought, after re-reading your latest post.

  1. You write "We measured all output signals of the Unitrol with changing the pf values." - Did you switch Unitrol into Power Factor control to change pf??
  2. If you can select PF control or manual excitation current control can you use this [after connection to bus" to get unit up to full load with acceptable power factor, avoiding trip?? This might be a strategy to "keep operating unit when essential" until problem is found and fixed.
  3. Usually, a control system will give an alarm (warning) for under-excitation before the trip level is reached. Say "underexcitation limiter working". Did you get an alarm??
  4. The only "output signal" of the Unitrol that matters is the DC field current to the generator. Can you measure this with instrument independent of Unitrol??
  5. If you can use independent ammeter, how does reading compare with Unitrol or control VDU/screen?? How does it compare with value on "well" machine??
  6. Purpose of field current check is to identify if Unitrol's own measurement of field current is bad. Also, to be sure generator itself is OK.
  7. Check manual, Unitrol may apply limiter by field current value, but trip by generator output current and voltage values.
Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#4

Re: Generator Reactive Power at Minus Values

12/23/2010 5:01 AM

Please see the generator power factor and adjust field current excitation because,

E = Va + jX*I
Since the magnitude of E is proportional to field current excitation, the leading power factor condition is sometimes referred to as under excited operation and lagging power factor condition is referred to as over excited operation for the synchronous generator.

For the under excited case, the generated reactive power is negative. This means that the generator machine is aborbing reactive power and is effectively operating as an inductor. For the over excited case, the generated reactive power is positive meaning that the machine is supplying reactive power and the machine appears as a capacitor.

Reply
Member

Join Date: Dec 2010
Posts: 5
#8
In reply to #4

Re: Generator Reactive Power at Minus Values

12/27/2010 10:50 AM

we tried this at first but we couldn't get any result

Reply
Participant

Join Date: Oct 2017
Posts: 1
#15
In reply to #8

Re: Generator Reactive Power at Minus Values

10/02/2017 2:19 AM

hello sir,

how are you

we also have approximately similar problem.we have three gen sets01 no is 2.5 mw 02 nos 4.0 mw &03 no is also 4 mw rating.

when we start the gen sets no 01& 2 on sharing mode than the reactive power control normal & power factor control also run normal position.but when we run the set no 01 & 3 in parallel in sharing mode than they are not control the reactive power means power factor automatically.we have to check the all cables & connections all is well.on avr display kvar & kw are not shown on avr no 01 & 03. but meters of panels kw &kvar showing normal.please suggest the remedy if any one knows about that;

thanks& kind regards

Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#16
In reply to #15

Re: Generator Reactive Power at Minus Values

10/04/2017 6:03 PM

I suggest you read all the comments on this question for ideas.

Since kW & kVAr are not shown on AVR 1 & 3, I would wonder if there is a common wire from their CTs giving line current to AVR 1 & 3 which is disconnected?

Also, when you write "are not shown on avr no 01 & 03", do you mean zero [0] is shown or just no number at all [spaces]. The software may be programmed not to put any "out of range, very positive or negative" number in display. A check on CT output volts on unit 3 compared to 1 & 2 for same panel meter readings is suggested. Track the CT signal right up to AVR terminals from CT terminals.

It would certainly be a good move to power down-up AVR 3 and, if that does not fix or report problem, then try checking/reprogramming to same parameters as 1 & 2.

There might be a physical connection to a "sharing" bus which is shorting the connection when AVR 3 switches-in, or maybe AVR3 sharing CT signal is not connecting to common bus. The bus may provide a mean kVAr to which each AVR matches, making kVAr equal (or equal part of rating) on each genset.

Reply Off Topic (Score 5)