Condenser Vaccum

12/26/2010 8:59 PM

Hi,

I have a problem where my vacuum transmitter and also manometer reads different measurement for the condenser vacuum.

during normal operations, vacuum reading from the transmitter will read at 900mBar but the manometer reads as 920mbar.

Both the instruments are located on the same level.

Any clues? fyi the tripping signal comes from the transmitter. The manometer acts as a secondary measurement.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#1

Re: Condenser Vaccum

12/27/2010 10:41 AM

If both instruments had a specified accuracy of +/- 1%, one read 1% high, the other 1% low - you would get a 20 degree difference. Look at the accuracy specifications for both instruments - I do not think you have a problem - unless you have a tripping setting of 910 mB!!

Register to Reply
Active Contributor

Join Date: Nov 2010
Posts: 18
#2
In reply to #1

Re: Condenser Vaccum

12/28/2010 4:33 AM

Hi,

can you elaborate further. Its true that we have +/-1% error accuracy specified.

But wont it give only +/-10mBar difference?

TQ

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3
In reply to #2

Re: Condenser Vaccum

12/28/2010 4:58 AM

If both instruments have +/- 1% accuracy, then One could be reading -10mbar while the other +10mbar! and the difference could be 20mbar max.

But what about Calibration? Normally, you need to calibrate these instruments. The transmitter and the Gauge could be brought to read near the same values if re-calibrated. The issue is how much precise you need the measurement to be:+/- 1% means that the error could be 20mbar. If narrower error is required, then instrument with 0.5% should be used.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#4

Re: Condenser Vaccum

12/28/2010 8:46 AM

Under normal conditions the manometer is considered a primary instrument that requires no calibration. Therefore you should adjust your transmitter to trip at the pressure indicated on the manometer. That way both instruments will agree at the trip point.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#5

Re: Condenser Vaccum

12/28/2010 11:08 AM

If you are using a mercury column type of manometer, then it is more accurate and should be used as the reference. Electronic manometer, its range and linearity readings should be calibrated based on the mercury manometer readings. That is of course assuming the mercury and its glass tube encapsulations are clean, is considered as the gold standard in pressure measurements.

__________________
vsar
Register to Reply
Power-User

Join Date: Apr 2010
Location: Moncks Corner, South Carolina, USA
Posts: 157
Good Answers: 6
#6

Re: Condenser Vaccum

12/28/2010 1:36 PM

Make sure you are using the liquid specified by the manufacturer in the manometer. The other consideration for manometers is that they should be installed where the ambient temperature is within the range specified by the manufacturer also. If you hang a manometer close to an uninsulated steam pipe this will cause the fluid density to change and affect the reading also too hot will cause the fluid to evaporate. As far as calibration, for a manometer with both ends exposed to the same (atmospheric) pressure it should read zero.

__________________
You can always tell a Nuke because you can't tell him anything!
Register to Reply Score 1 for Good Answer
Member

Join Date: Dec 2010
Location: Lahore ,Pakistan
Posts: 9
#7

Re: Condenser Vaccum

02/07/2011 12:20 AM

Dear ,

You did not mention trip setting of transmitter.If your are talking about turbine condenser ,then you need a little worry.You need to describe some process detatil also.

Akram

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); fadzril (1); LAA_Lucke (1); M.Akram (1); vsar (1); welderman (1); XNuke (1)

Previous in Forum: Natural Gas Meter Sizing   Next in Forum: Mini Projects - Control System

Advertisement