HT Installation Safety

01/05/2011 4:19 AM

How safe is testing the accuracy of the meter in a HT installation? The meter is in a Metering Cubicle and that's where the Ammeter,Voltmeter, 5A CT's and 110VT's are connected.

Is there extra pre-cautions that should be adhered to?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: HT Installation Safety

01/05/2011 4:42 AM

Under no circumstances should the CT's be open circuited unless the metered feeder is isolated.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 3)
Associate

Join Date: May 2010
Location: RSA
Posts: 33
#5
In reply to #1

Re: HT Installation Safety

01/10/2011 7:08 AM

Noted, thanks.

Register to Reply
Participant

Join Date: Dec 2010
Location: Pakistan
Posts: 1
#2

Re: HT Installation Safety

01/06/2011 11:59 PM

Hello dear,

Its too dangerous and harmful to do so. You should be careful about these kinds of jobs and please do it after switching off the circuit. U may calibrate meters from a specialist for accuracy.

Now its up to you how you care yourself such practices should be done by experts there is a possibility of insulation damage too.

__________________
Little bit In Electrical Tecnology...!!!
Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3

Re: HT Installation Safety

01/07/2011 3:48 AM

Not safe for an amateur! You are going to be very near to the HT points: The VT's and CT's are on the HT Cables or Bars!

The Meter is connected to these CT's and VT's, and should be away from the HT lines (reasonably with in the cubicle).

All you need to calibrate is the meter (usually). For this you need to compare its reading with a calibrated instrument (another meter) that needs to be wired to either the same CTs VTs or different ones. To do the connections, you need to Isolate the Supply from the HT side before all this is done.

Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#4

Re: HT Installation Safety

01/10/2011 6:26 AM

Short the metering core and disconnect the meters form the CT secondaries and you can test the accuracy with kits like phantom loading kit or any calibrated equipments.Make sure not to open the CT secondaries when it is live.

For VT remove the fuse and disconnect the meters and continue with the testing. Make sure a qualified engineer carryout this to avoid accidents. Bcoz, CT is the most dangerous equipment in electrical systems. It is danger for itself as well as you with its lethal voltage in secondaries when it is open.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

hhhunzai (1); LAA_Lucke (1); TonyS (1); vijaymail_electrical (1); WisdomJD (1)