Demand Factor Question?

01/12/2011 12:18 PM

So I am looking at some initial investigation on a new design/addition to a existing building and have a quick question regarding demand factor

This is T14 in Ontario Electrical Code

--------demand factor %%------

Office w/m2 service conductor feeder

< 930m2 50 90% 100%

> 930m2 50 70% 90%

Hope this makes sense. My question is what is demand factor? If I have a Base Load of i.e. 100kW and results in a Amperage of 277A 3PH 4 WIRE 208V . Does demand factor of 70% allow me to "downsize" my service a maximum to 70% of calculated?

Thank you fro the guidance in advance.

Woz!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Demand Factor Question?

01/12/2011 2:45 PM

Yes, but No... as in all things, answers are not cut and dried.

Table 14 speaks to the watts per square meter and demand factors allowed for service conductors and feeders for various types of occupancies.

All "Office" areas have a basic load of 50 watts per sq meter.

As per CEC rule 8-210(b), other loads that may be in the office area such as electric space-heating, air-conditioning, power loads, show window lighting, stage lighting, are not included in that 50 watts per sq meter value.

So... given an office area of 1200 m2... (not inside another facility).

First 930 m2 = 930 x 50w = 46,500w of base load.

Service demand factor for the first 930 m2 is 90%

So the first 920 m2 contributes...

46,500w x 0.9 = 41,850w of minimum service ampacity

For the remaining area...

1200 - 930 = 270 m2

270 x 50w = 13,500w of base load.

Service demand factor for the remaining area is 70%

13,500w x 0.7 = 9,450w of minimum service ampacity

So the contribution to the minimum ampacity of the service is...

41,850w + 9,450w = 51,300w for the office portion of the service.

You must add any other demand based on other equipment, as mentioned above minus any demand factors allowed by other areas of the code for that additional equipment.

For an office area "inside" another occupancy fed by a feeder and not by "service conductors", follow the same process only using the 100% and 90% values as indicated in the table.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2009
Posts: 99
#2
In reply to #1

Re: Demand Factor Question?

01/12/2011 3:13 PM

ahhhh, thank you sir.