If Broken or Loose Grounding of Link Box

01/12/2011 12:54 PM

if broken or damage or loose grounding in splice joints location of 132 kv in link box for fault current and distance is 3 km of UG cale line between have have four link box two or three condition for grounding which above mentioned whole line will trip or fault will come

Register to Reply
Pathfinder Tags: broken or damage grounding
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#1

Re: If Broken or Loose Grounding of Link Box

01/12/2011 1:38 PM

Please break your message into brief parts. Use CR4 "1,2,3.." list

  1. 132 kV cable has four joints.
  2. Each joint is in a link box.
  3. 3 km length between each joint.

or bullet

  • aa
  • bbb
  • ccc

Question not clear, at present. Question part ends with ?

Register to Reply
Active Contributor

Join Date: Jan 2011
Posts: 11
#2

Re: If Broken or Loose Grounding of Link Box

01/14/2011 5:21 AM

sir if spluice joint area broken due to excavation or loose grounding in link box what will problem create

irfan

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3
In reply to #2

Re: If Broken or Loose Grounding of Link Box

01/14/2011 10:51 AM

I think you mean to write (using the 1--2--3-- button at top of CR4 message box):-

If :-

1. Area around a cable joint is broken-up by excavation, or

2. Grounding inside a link box is lose.

- what problems will be created. If I am right, following are my answers to 1 and 2. I am not a High Voltage specialist, but some general facts apply.

1. Sharp stones can be pressed onto cable causing damage. When local ground has sharp stones, it is necessary to fill excavation with fine material close to cable to protect cable. Ground thrown in loose will not conduct heat and cool cable as well as normal ground. It needs to be "compacted" mechanically to restore normal state. Early failure of cable or shortened life will be caused when correct filling is not done.

2. "In" or "inside" a box grounding or earthing is not the word. Bonding, meaning "joining together" electrically is what is important. The voltage drop along a cable, during a short circuit is considerable. Especially when the cable is long and the electrical source is strong, a very large voltage can appear along a cable if there is a short circuit at its end. The cable metal sheath is the main return path to to the generator. When the box is locally earthed, there could be a dangerous voltage between box and cable, if they were not bonded together. When there is a link in a box, to give access for testing, then bonding between the sheaths of cables entering it would be vital to carry ground fault current currents.

3. Perhaps you mean boxes in which all 3 phases are brought together and the sheath bonding joins the 3 sheaths together? In this case the currents between the sheaths may not be small in normal operation and a loose connection could overheat or spark. Sometimes, due to errors in design, particularly long runs, the circulating currents are excessive and overheating occurs, causing failure of the cable at the box.

I hope this helps, Irfan.