Type Tests

01/19/2011 9:22 AM

Is it required all the type tests to be carried out in same Switch gear( MV and LV switchgears) as per IEC/BSEN standards? For example, few type tests are done on Switchgear #A and other tests on Switchgear B. But the Panels for the Project are manufactured as per the same configuration of A and B. Is that normal procedure in switchgear industry?...

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Type Tests

01/19/2011 12:29 PM

That's what type test means - Testing is done on one unit which represents the common design for a "type" of equipment, and the results are valid for all the units of that "type." Thus the use of the word "typical" to mean valid for all of a certain type.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Anonymous Poster
#2
In reply to #1

Re: Type Tests

01/19/2011 10:05 PM

Thanks. I will register and give GA.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Type Tests

01/19/2011 11:17 PM

If you mean whether all type tests are to be carried out on the SAME sample, the answer is no. For example, a LV circuit breaker needs to be tested as per IEC 60947-1&2, where at least 4 test sequences are to be followed to certify the Circuit Breaker. Normally 4 to 6 samples undergo different tests.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#4
In reply to #3

Re: Type Tests

01/20/2011 6:32 AM

Ok. I understand. Where can I find the supporting documents including the standards as like clause no etc?..Just give me a hint. I will find out. I have to support supplier to fight with consultant

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Type Tests

01/20/2011 6:50 AM

i already gave - IEC 60947- part 1 and 2 for Circuit Breakers. If you are in India, you can use IS 13947 - 1 and 2 which are identical and far cheaper. You can also ask CPRI and ERDA, who are testing authorities in India.

One advice - never fight with a consultant. He can always throw a spanner in the works.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Type Tests

01/20/2011 7:43 AM

KVS, I think IS 13947 is renamed (or is it re-numbered) as IS 60947, to be in line with IEC. Pl. confirm. I very recently received a mail from my seniors in this regard.

Reply
Anonymous Poster
#7
In reply to #5

Re: Type Tests

01/21/2011 11:58 PM

As per your suggestion, I read the following standards in the last three days.

1.IEC 60947-part 1 LV switchgear - geberal

2.IEC 60947-part 2 - Circuitreakers.

3.IEC 60694-Highvoltage switchgear and control

and the below mentioned Type Test standards

4. IEC 61436 part 1 to 7 for LV switchboards, Busbars.etc

5. IEC 60227-200 for MV switchgear.

I could not find (or understand) anywhere it said that multiple samples are required mandatory for type testing.

Sir, could you give me more clarification on this reagrds.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: Type Tests

01/22/2011 12:43 AM

i give a small extract of Table X of IS 13947-2. You will notice that tests are specified on sample 1, sample 2 etc. This is a small part of the table, you will get more data from the IEC.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#9
In reply to #8

Re: Type Tests

01/22/2011 3:59 AM

Thank you. I saw almost similar to this in IEC.

Reply