Reverse Reactive Power

01/23/2011 10:34 AM

I have Three Main Power Gas Turbines rated at 6000kVA, 3.3kV and also Three Diesel generators rated at 2500kVA, 660V. We have a problem with Diesel Gen 2 when synchronised with Main Power Turbines, it causes Main Power Turbines to go into reverse reactive power, which is not healthy for the machines. This has happen twice and the other Diesel Gen 1 and 3 dont have this problem. What do I need to do to fix this problem?

Regards

bavuman (South Africa)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Reverse Reactive Power

01/23/2011 11:56 PM

Your premises are incorrect, and your thinking about the problem foggy at best. Let's review: in any network, and the power distribution network is such, there are imbalances.

If your local generator working against the network is in phase and produces higher voltage, it is a net energy supplier. If its voltage is lower, it is a net energy consumer.

If your local generator voltage is equal that of the net, leading phase produces current when the net does not = inductive virtual power. Lagging phase = capacitive virtual power.

Since most loads are resistive and inductive, a corrective balancing is frequently required by the energy producer. They charge extra for the customer for their trouble, producing the necessary, mostly capacitive correction using their power generators.

I repeat, reactive power is NORMAL for a generator. Your generators working against each other is not. Fix their phase relationships, and they and you will be a happy camper.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Reverse Reactive Power

01/24/2011 7:26 AM

Assuming you do not have a mains connection, it looks as if Gen2 voltage is going high and taking all the reactive power and more. If sudden event correcting itself, may be loss of AVR reference or AVR fault. Monitor field current of Gen 2 with DC meter and see if it jumps high when turbines go reverse. High field current increases lagging output of a generator if bus voltage stays normal.

Register to Reply Score 1 for Good Answer