Anonymous Poster

Cable Installation from VFD to Dynamic Braking Resistor

01/31/2011 7:07 PM

The dynamic braking resistor dissipates regenerative power during braking the motor by braking chopper. Single conductor cables are used for VFD to Braking Resistor. It is DC circuit. The braking chopper triggers on and off repeatedly due to actual operation. The DC cable installation is not limited to any special requirement in bunching cables or laying cables. However, someone says that IEC 60092-352 should be applied because braking chopper is on/off, on/off,....

IEC 60092-352 is applicable to single conductor cables installation for 3 phase AC circuit. is it right if this cables are applied to IEC60092-352 like AC circuit ? I am against that because repeated on/off does not drop below zero.

Help me

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Cable Installation from VFD to Dynamic Braking Resistor

02/01/2011 1:48 PM

IEC60092-352 appears to specifically relate to electrical wiring installations on ships.

I do not have a copy of the standard (which doesn't help), but what exactly is the IEC60092-352 requirement(s) that you are trying to avoid in your particular application? Cable sizing perhaps? Just how far are the breaking resistor(s) from the drive?

Who is this someone, and what does your overall specification say. If it is only going to increase the cost a little then it may be worth installing the DC breaking resistor wiring to IEC60092-352, especially if the (client) believes so or there is a possibility you may need to modify your wiring later to meet IEC60092-352 (at your expense).

A close look through IEC60092-352 may shed more light on your question.

__________________
jack of all trades
Reply