Hello,
In my opinion in three phase-three wire radial network system, during phase to ground fault voltage of faulty phase drops zero and phase to ground fault of healthy phase increases.
But if we want to prevent embedded generator operating in island mode because of an earth fault of anywhere in network we must provide selective current protection.
We can't provide this protection with overvoltage or undervoltage protection?
What is your opinion and suggest?
Best Regards,
Musa UÇAN
Good Answers: 170
Re: Embedded generator earth faulth protection
02/03/2011 5:25 AM
But, there could be over voltage or undervoltage in the system even when there is no earth fault. If you use a voltage relay for earth fault, how will you deduce the cause of the tripping?
Re: Embedded Generator Earth Fault Protection
02/03/2011 11:06 PM
For earth faults you have to select graded earth fault protection relays 50G / 51G, who told you to use "selective current protection".
Knowledge sharing is a WIN-WIN situation
02/04/2011 1:50 AM
Dear Mountk2,
In radial network earth fault may occur on anywhere....
Our aim to prevent operating generator in island mode.
If earth network occurs in fider which feed unearthed transformer ( DD ) about load side ( not source side ).
So earth fault current will flow on faulty conductor and return to the source from healthy conductor. Because there is no earth conductor...
Best Regards,
Musa UÇAN