A soft starter is a solid state motor starter that is used to start or stop a motor by notching the voltage waveform, thereby, reducing the voltage to each phase of a motor and gradually increasing the voltage until the motor gets up to full voltage/speed all at a fixed frequency. The profile of the increase of voltage depends on the application. The voltage is reduced and controlled by 3 pairs of back-to-back silicon-controlled rectifiers (SCRs), which are a type of high speed thyristor. A soft starter takes the place of a contactor and can also take the place of an overload relay in a standard motor starting application.
In general, there are two reasons to use a soft starter: the power distribution network may not be able to handle the inrush current of the motor and/or the load cannot handle the high starting torque. As a rule of thumb, a motor utilizes around 600-800% of its full load current (FLA) to start. This current is referred to as inrush current or locked-rotor current. If a large motor is on a smaller power distribution network or on a generator system, this inrush current can cause the system voltage to dip, or to "brown out". Brown outs can cause problems with whatever else is connected to the system, such as computers, lights, motors, and other loads. Another problem is that the system may not even be able to start the motor because it cannot source or supply enough current. Most industrial businesses run during the day can be fined or charged extra (Peak Demand charges) during this peak usage time for large transients caused by large horsepower (HP)/Kilowatt (kW) motor start ups. These Peak Demand charges can add up very quickly, especially if the motor needs to be started multiple times during any given day. The inrush current can be controlled one of two ways with a soft starter: either with a current limit (discussed later) or reduced linearly with the reduced voltage, and follows this approximation:
Applications such as conveyors may not be able to handle a sudden jolt of torque from an across-the-line start. Utilizing soft starters reduces the wear and tear on belts, conveyors, gears, chains, and gearboxes by reducing the torque from the motor. The torque decreases as a square of the reduced voltage, and follows this approximation:
Since soft starters are generally controlled and monitored by a microprocessor, a soft starter can add many features and protections fairly easily. It can offer a choice of the starting time, limited speed control, and energy savings. Power monitoring, such as three-phase current, three-phase voltage, power, power usage, power factor, and motor thermal capacity usage, can be implemented with current transformers, a voltage meter, and an internal clock. With the above implementations, protection, for the motor or the soft starter, from the items listed below (Table 1) can also be offered by stopping the firing of the SCRs, dropping out the bypass contactor (a contactor that carries the motor load after the motor is up-to-speed), and/or alerting a user via some form of communications with the microprocessor and another computer.
__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)