Harmonic Distortion in Supply Line

02/17/2011 3:43 AM

Hi,

What are the techniques to Cater harmonic distortion in Supply line?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Harmonics

02/17/2011 4:00 AM

Did you heard of distribution factor Kd?

Register to Reply
Anonymous Poster
#2

Re: Harmonics

02/17/2011 4:42 AM

go for linear filters circuits... if you have too much harmonic content then go for SVC (Static VAR Compensators). they are known to suppress harmonics to a large extent at the same time they are very expensive..

Register to Reply
2
Active Contributor

Join Date: Feb 2011
Location: Pakistan
Posts: 18
Good Answers: 2
#3
In reply to #2

Re: Harmonics

02/17/2011 5:34 AM

General Solutions to the harmonics problem are:

Special Transformers:

There are several special types of transformer connections which can cancel harmonics. For example, the traditional delta-wye transformer connection trap all the triplen harmonics (third, ninth, fifteenth, twenty-first, etc.) in the delta. Additional special winding connections can be used to cancel other harmonics on balanced loads. These systems also use more copper. These special transformers are often specified in computer rooms with well balanced harmonic producing loads such as multiple input mainframes or matched DASD peripherals.

K-rated transformers are also used to accomodate additional heat caused by harmonics I.

Filtering:

special electronic tracking filters can work very well to eliminate harmonics. These filters are presently relatively expensive but should be considered for thorough harmonic elimination.

The Hershey Solution:

The standard Hershey System incorporates broadband harmonic filtering to mitigate the effects of harmonics in the system and render them to a harmless level, thereby helping to release KVA capacity in the transformer, while protecting conductors from overheating, improving the operation of plant equipment and reducing the losses caused by the harmonics.

This is accomplished through the application of variable, non-saturable, zig-zag reactors both at the source of the harmonic currents (load) and at the transformer in the mainframe unit. Furthermore, if harmonics of excessive magnitude exist, optional specific harmonic filtering can be employed.

Oversizing neutral conductors:

In three phase circuits with shared neutrals, it is common to oversize the neutral conductor up to 200% when the load served consists of non-linear loads.

Register to Reply Good Answer (Score 2)