Power Factor Improvement For D.g Set

02/26/2011 6:38 AM

can we connect capacitor bank after d.g set?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: power factor improvement for d.g set

02/26/2011 7:00 AM

No please dont do it

Reply Score 1 for Off Topic
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#2

Re: Power Factor Improvement For D.g Set

02/26/2011 8:54 AM

If you ask something, please decribe it completely !

__________________
One system
Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3

Re: Power Factor Improvement For D.g Set

02/26/2011 9:22 AM

Yes. For what purpose? Presumably for power factor control? (Ahh, yes--I should have read the title of the thread.) It would be the same as power factor control capacitors used anywhere else.

I would question whether you really needed them--I wouldn't expect your "transmission lines" to be that long that you'd save significant money by switching to smaller cables.

Hmm, on the other hand (I'm not a generator expert), maybe you'd get more power out of the generator (kilowatts) if the generator isn't also generating kvars--I'm assuming the kvars would add heat to the windings...

Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#5
In reply to #3

Re: Power Factor Improvement For D.g Set

03/01/2011 8:23 AM

After more thought, I'm certain that the kvars (or the current flow due to the kvars) will add to the heat rise in the generator windings. If you could get rid of the kvars in the generator (i.e., supply the kvars from power factor correction capacitors external to the generator (where else would they be ;-)), you will be able to get more kilowatts out of the generator.

So, it my indeed make sense to add p.f. capacitors.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Power Factor Improvement For D.g Set

03/01/2011 3:46 AM

Please refer to an earlier thread on the subject I had published a detailed paper on the subject in that thread.