03/03/2011 1:16 AM

Need to do repair & service work in manhole with 12.5kV cables (10 energized, 1 dead). What rules & procedures do you use for this. No splices there & all cables are triplexed shielded single conductors, over-wrapped. All exposed metal is bonded. Cables date to 1970. Will replace sump pump & its disconnect, muck out bottom of manhole, and see if transite duct to next manhole is intact for new cable installation. My thoughts: before entering pump out water (some cables immersed now), blow air in to dry, wear 40cal arc flash suit until cables covered with rubber blankets, then do other work. De-energizing all cables is a very remote possibility. Utility delivers power at 12.5kV & we then distribute 12.5kV to various buildings from central plant, with substations in each building. We would also follow standard confined-space entry procedures (USA).

Register to Reply
Pathfinder Tags: manhole MV cables safety
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Work in manhole with energized cables

03/03/2011 5:17 AM

Cables of that age will most likely be lead sheathed so water shouldn't be a problem. But try to avoid moving them in any way.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#2
In reply to #1

Re: Work in manhole with energized cables

03/03/2011 7:40 AM

TonyS,

Where they enter the switchgear, I do not see any lead. Thanks for the input.

--JMM

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Work In Manhole With Energized Cables

03/03/2011 9:53 AM

What level of protective clothing are you planning after the cables are blanketed? I know that 40cal is bulky and hard to work in, but even blanketed, there is significant hazard from a flash/blast. Even blanketed, the requriement for the 40cal might not be relaxed.

Be sure you run an air monitor to measure O2 levels as well as possible noxious gases. I assume this would be part of your confined space procedures, as would be the use of an external rescue system (tripod, winch/cable, and harness) to pull out an unconscious worker if for some reason he were to collapse. Safety first!

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5
In reply to #3

Re: Work In Manhole With Energized Cables

03/03/2011 2:39 PM

PeterT (& also KJK/USA),

Site is pretty strict about following confined space rules. Already opened lid to look in (but not enter), then closed after look/see. O2 is 20.8%, % LFL 0.0, CO 0.0%, H2S 0.0%. We will use a tripod & harness, of course.

We have 40cal and 12cal suits, plus 15kV gloves. We have not calculated available fault energy, but suspect is would be quite large. However, with concentric shielded cables, wouldnn't a fault through the dielectric be mostly (if not entirely) confined within the cable? I'm hoping someone could cite rules or policies that are in place where they work, regarding these questions. Range of policies can be from no entry until all cables de-energized & locked-out, to . . . . If shutdown is required, the problem is in trying to plan or schedule any outage long enough to do some work. If that's what has to be done, then that is what we will do; however, I always like to explore the range of possibilities or options before proceeding.

I find it hard to conceive of an installation with a sump pump that requires occasional service and allowing that only with a complete shutdown of a facility that runs 24/7.

Thanks--JMM

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#4

Re: Work In Manhole With Energized Cables

03/03/2011 1:44 PM

Along with the great suggestions above, you may also want to consider one of these.

They are ABSOLUTLY required in my local.

Be safe!

Link: http://www.northernsafety.com/Product/162-7738/DBI-SALA-Confined-Space-7-Two-Way-Tripod-and-Salalift-Winch-System-with-1-4-x-60-Cable

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Work In Manhole With Energized Cables

03/03/2011 3:37 PM

Do you open the re closing circuit to the breaker(s) that feeds these cables?

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #6

Re: Work In Manhole With Energized Cables

03/04/2011 5:11 PM

wareagle,

I assume you are talking about utility line automatic reclosers. This is a customer-owned and customer-maintained site. All breaker operations are manual, with lockout & tagout procedures in place and working.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Work In Manhole With Energized Cables

03/04/2011 1:44 AM

Mechnical protection of the cable is not a UK requirement but the manholes I've been down, we've used 1 inch marine ply to lay over the cables to offer a further degree of protection to the cables. It stops dropped tools damaging the outer sheath of the cables..

__________________
The square root of nothing is what you make it!
Register to Reply
Associate

Join Date: Dec 2006
Posts: 27
#8

Re: Work In Manhole With Energized Cables

03/04/2011 7:27 AM

How much work can be completed without going into the hole?

use vacuum device clean and dewater

use camera to perform inspection

if work involves feeding through the manhole can you excavate outside and intercept the conduits you need to use?

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#12
In reply to #8

Re: Work In Manhole With Energized Cables

03/04/2011 5:19 PM

Thanks, Natfuelbill,

The manholes are nominally 6'x6'x9'deep. Sump pumps are hard-wired with cords, no plugs; discharge piping cannot be disconnected without being on the fixed rungs in the manhole. Duct bank is concrete encased, so interception is not possible. Inspection with a camera may be possible, but snaking a camera into a duct bank opening 7-8' below and then working with it may be difficult. Clean & dewater with vacuum (and hose to wash muck to vacuum pickup) is a good idea.

--JMM

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#9

Re: Work In Manhole With Energized Cables

03/04/2011 11:18 AM

I have found the best resource is your utility supplier for procedures to handle the job like you've outlined. There are others out there that do high voltage maintenance etc;. I would suggest that given the question you are asking I would contact an outside party to make these repairs. It would be much safer for you and the employees who might be called on to preform a task they are not familiar with.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #9

Re: Work In Manhole With Energized Cables

03/04/2011 12:14 PM

I like your answer.. GA from me...

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (2); fixitorelse (1); jmueller (4); KJK/USA (1); Natfuelbill (1); PeterT (1); TonyS (1); wareagle (1)

Previous in Forum: Is There Any Governing Body that Certifies Labs?   Next in Forum: Dimensions of Lab Layout

Advertisement